[BLDG-SIM] eQuest/DOE-2.2 User's Group
Chris Jones
cj at cr-jay.ca
Thu Feb 6 06:45:09 PST 2003
That is interesting. The LEED Gold project I simulated required some
modifications (from the LEED reviewer) that could not be done with HAP,
etc. Only a 3D capable program could do what I was required to do using
DOE2.1e. I could have done the same with DOE2.2.
I stand corrected on ASHRAE 90.1 - From Section 11.2.1: "(a program such
as, but not limited to, DOE-2 or BLAST)".
I am glad to find such an informed email list.
>Eric is absolutely correct! DOE2 is not required nor is it the only
>available software that meets data submission requirements. ASHRAE and the
>U.S. Green Building Council (USGBC) do not officially sanction or certify
>software programs. As for LEEDS, the USGBC only determines the
>acceptability of data for LEED project submissions. Other commercially
>available software programs such as Carrier Corporation's HAP meet all
>data acceptability requirements of LEEDS and the ECB method from ASHRAE
>90.1-2001.
>
>Regards,
>
>Craig J. Gann, P.E.
>----- Original Message -----
>From: <mailto:christensen at econergy.net>Eric Christensen
>To: <mailto:BLDG-SIM at GARD.COM>BLDG-SIM at GARD.COM
>Sent: Wednesday, February 05, 2003 2:02 PM
>Subject: [BLDG-SIM] eQuest/DOE-2.2 User's Group
>
>I am not a definitive authority, but I do not believe that ASHRAE 90.1 or
>LEED requires DOE-2.1e exclusively. Section 11.2.1 of 90.1-1999 & 2001
>requires "a program such as, but not limited to, DOE-2 or BLAST." It then
>outlines required capabilities of the simulation program. eQUEST is DOE-2
>based, so I believe that it is acceptable for 90.1 compliance and LEED scoring.
>
>Eric Christensen
>Econergy International Corporation
>3825 Iris Avenue, Suite 350
>Boulder, CO 80301
>Phone: (303) 473-9007
>Fax: (303) 473-9060
>E-mail: christensen at econergy.net
>Website: www.econergy.net
>-----Original Message-----
>From: postman at gard.com [mailto:postman at gard.com]On Behalf Of Chris Jones
>Sent: Wednesday, February 05, 2003 12:22 PM
>To: BLDG-SIM at GARD.COM
>Subject: [BLDG-SIM] eQuest/DOE-2.2 User's Group
>
>We use DOE2.1e in our shop. Primarily because of the significant
>verification against measured data that has been done on DOE2.1e over the
>years. The other reason is that ASHRAE 90.1 and in particular LEED
>require simulation using DOE2.1e.
>
>Here in Canada, the Model National Energy Code, Performance Option
>required simulation using EE4 (a free compliance tool http://www.ee4.com )
>that used the DOE2.1e engine from Hirsh and Associates. Similar to
>eQuest, you can use EE4 to quickly generate an input file then edit it for
>you particular situation.
>
>
>
>
>
>
>
>
>
>>We use eQuest extensively, sometimes using the wizard mode to get
>>started, sometimes not. We began using DOE2.1d when it was first
>>available on PC platforms and kept with it through PowerDOE and the
>>`never officially released DOE2.2. We often use eQuest to create BDL code
>>which we then edit with a text editor. I must admit I m sometimes
>>surprised to hear of modelers (often in Academic situations) still
>>working with 2.1e when `2.2 is a significant improvement and is
>>absolutely free via eQuest.
>>I, like John, am holding off on EnergyPlus until I can justify the
>>tremendous expense of training my people on a new product that is still
>>not ready for prime time. Eventually, I hope, but not yet. I m guessing
>>five years before there is a product that is enough better than eQuest to
>>justify the investment. (And that s assuming eQuest doesn t continue to
>>improve).
>>I imagine that there are numerous eQuest users that are not aware of the
>>BLDG-SIM forum. Too bad it would be nice to see more interaction around
>>the eQuest program. Perhaps SCE/EDR could provide an information blurb
>>about this forum on their web site or to everyone who down loads eQuest.
>>
>>
>>Mark E. Case, P.E.
>>etc Group, Inc.
>>Salt Lake City, Utah
>>
>>-----Original Message-----
>>From: postman at gard.com [mailto:postman at gard.com] On Behalf Of Mike Roberts
>>Sent: Tuesday, February 04, 2003 1:03 PM
>>To: BLDG-SIM at GARD.COM
>>Subject: [BLDG-SIM] eQuest/DOE-2.2 User's Group
>>
>>John,
>>
>>There are at least a few of us out here using eQUEST/DOE-2.2 on a regular
>>basis. I started using DOE-2.1 back when it was Cal-ERDA 1.3 (about
>>1979) and have followed the Hirsch upgrades through PowerDOE and
>>eQUEST. I have only seen a Beta version of eQUEST 3.0, but it looks very
>>interesting.
>>
>>My specialty is energy simulation and I use eQUEST and the "Detailed Data
>>Edit" Mode on almost all of our energy simulation jobs. JJ Hirsch and
>>Associates are looking for ways to offer more support, but probably at a
>>price. I can offer some support, free if it is trivial (to me) or at my
>>regular rates if it is more involved. Our web site is
>><http://www.roberts-engineering.com/>http://www.roberts-engineering.com/.
>> Hopefully, you will find some useful information there.
>>
>>I think the User Group is a good idea, though you already have a
>>discussion forum through
>><mailto:BLDG-SIM at gard.com>BLDG-SIM at gard.com. Let me know how much
>>interest you get.
>>
>>Mike
>>-----Original Message-----
>>From: postman at gard.com [mailto:postman at gard.com]On Behalf Of Aulbach, John
>>Sent: Tuesday, February 04, 2003 11:43 AM
>>To: BLDG-SIM at gard.com
>>Subject: [BLDG-SIM] eQuest/DOE-2.2 User's Group
>>May I ask how many people are attempting to use eQuest/DOE-2.2? I would
>>like to form a User Group for exchanging questions and war stories, as
>>the creators of the program do not apparently have funding for very much
>>support (Sad).
>>I have taken Marlin Addison's a few times, with the last version I have
>>(3.0) FINALLY beginning to make sense. I have used DOE-2.1 since 1984 and
>>have some small familiarity with the intent, switches, and boundaries of
>>the program. Until a decent front end come along for EnergyPlus, this is
>>the way I am going.
>>There claims to be over 7,000 downloads of the program. Anyone getting
>>into the "world past the Wizards" yet?
>>
>>John R. Aulbach, PE, CEM
>>Project Engineer
>>Sempra Energy Solutions
>>555 West Fifth Street
>>Mail Location 27F3
>>Los Angeles, CA 90013
>>Tel: (213) 244-8551 Cell (213) 219-4875
>>
>>
>>
>>"Sempra Energy Solutions is not the same company as SDG&E/ SoCalGas, the
>>Utilities. Sempra Energy Solutions is not regulated by the California
>>Public Utilities Commission, and you do not have to buy Sempra Energy
>>Solutions products or services to continue to receive quality regulated
>>service from the Utilities."
>>
>>
>>
>>
>>
>>
>>
>>==================
>>
>>You received this e-mail
>>because you are subscribed
>>
>>
>>to the BLDG-SIM at GARD.COM
>>mailing list. To unsubscribe
>>
>>
>>from this mailing list send
>>a blank message to
>>
>>
>>BLDG-SIM-UNSUBSCRIBE at GARD.COM
>>etc Group, Inc. 3481 South 2300 East, Salt Lake City, Utah
>>84109 (801) 278-1927, FAX (801) 278-1942
>>
>>Normal.dot 2/4/2003 2:33 PM
>>
>>etc Group, Inc. 3481 South 2300 East, Salt Lake City, Utah
>>84109 (801) 278-1927, FAX (801) 278-1942
>>
>>Normal.dot 2/4/2003 2:33 PM
>>
>>etc Group, Inc. 3481 South 2300 East, Salt Lake City, Utah
>>84109 (801) 278-1927, FAX (801) 278-1942
>>
>>Normal.dot 2/4/2003 2:33 PM
>>
>>etc Group, Inc. 3481 South 2300 East, Salt Lake City, Utah
>>84109 (801) 278-1927, FAX (801) 278-1942
>>
>>Normal.dot 2/4/2003 2:33 PM
>>
>>etc Group, Inc. 3481 South 2300 East, Salt Lake City, Utah
>>84109 (801) 278-1927, FAX (801) 278-1942
>>
>>Normal.dot 2/4/2003 2:33 PM
>>
>>etc Group, Inc. 3481 South 2300 East, Salt Lake City, Utah
>>84109 (801) 278-1927, FAX (801) 278-1942
>>
>>Normal.dot 2/4/2003 2:33 PM
>>
>>etc Group, Inc. 3481 South 2300 East, Salt Lake City, Utah
>>84109 (801) 278-1927, FAX (801) 278-1942
>>
>>Normal.dot 2/4/2003 2:33 PM
>
>
>Chris Jones, P. Eng.
>14 Oneida Avenue
>Toronto, ON M5J 2E3
>Tel. 416 203-7465
>Fax. 416 203-8249
>
>
>
>
>==================
>You received this e-mail because you are subscribed
>to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
>from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
>
>
>You received this e-mail because you are subscribed
>to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
>from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at GARD.COM
Chris Jones, P. Eng.
14 Oneida Avenue
Toronto, ON M5J 2E3
Tel. 416 203-7465
Fax. 416 203-8249
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20030206/5a6c94b3/attachment-0002.htm>
More information about the Bldg-sim
mailing list