[BLDG-SIM] LEED / ASHRAE 90.1 Modeling Question
Marcus Sheffer
sheffer at paonline.com
Mon Jun 2 09:04:13 PDT 2003
We will be submitting some shortly and this is how we have interpreted the
CIRs. Schedule changes are acceptable is my understanding. The adopting
authority in this case is the USGBC and they have stated that schedule
changes are allowable for DCV. To be 100% sure, develop your methodology
for calculating savings and submit it as a CIR.
At 11:47 AM 06/02/2003 -0400, you wrote:
>Thanks for your reply.
>
>I re-read a CIR from 6/7/2001 (perhaps the one to which you are
>referring?) to be sure that I hadn't missed anything. In the Project
>Manager's Ruling, it says:"Under the ECM [Exceptional Calculation Method],
>schedule variations may be used as a basis of engineering calculations for
>discrete measures that are precluded by the reference standard or the
>LEEDTM EMP."
>
>However, the description of the ECM in section 11.5 of the 90.1 manual
>states that the applicant must provide documentation supporting the
>accuracy of the exceptional method and that "This documentation must also
>show that the methods and its results:
>1. Do not change the simulation program input parameters that are
>constrained by the ECM method or any other rules of the adopting
>authority. For example, the exceptional method may not violate the rule
>against using different operating schedules for proposed and budget runs."
>
>So it is still unclear to me whether or not schedule changes are
>acceptable. Have you successfully proposed schedule changes such as these
>through the ECM process?
>----- Original Message -----
>From: <mailto:sheffer at paonline.com>Marcus Sheffer
>To: <mailto:wmclaughlin at dmiinc.com>wmclaughlin at dmiinc.com
>Cc: <mailto:BLDG-SIM at GARD.COM>BLDG-SIM at GARD.COM
>Sent: Monday, June 02, 2003 11:04 AM
>Subject: Re: [BLDG-SIM] LEED / ASHRAE 90.1 Modeling Question
>
>I'd suggest you review the CIRs more closely. DCV has been approved as an
>energy saving measure and you can modify schedules to simulate
>savings. You must follow the Exceptional Calculation Method (section
>11.5) of the Energy Cost Budget Method of 90.1.
>
>At 10:14 AM 06/02/2003 -0400, you wrote:
>>Hi All,
>>
>>We are currently working on our first LEED certification project. We use
>>PowerDOE as a modeling tool, but these questions should apply to all
>>modeling platforms.
>>
>>The LEED process requires modeling practices to follow those outlined in
>>the ASHRAE 90.1 Standard User's Manual. The standard does not allow for
>>the augmentation of schedules to model efficiency measures. This is a
>>problem for us in that we often use schedules to simulate measures such
>>as lighting occupancy sensors and demand controlled ventilation.
>>
>>Typically:
>>-For lighting occupancy sensors, we adjust our known office schedules
>>using a profile taken from the JIES (I'm afraid I don't have the specific
>>source in front of me).
>>-For demand controlled ventilation, we develop an hourly outside air
>>Fraction of Design schedule for each AHU using known occupancy schedules
>>and an assumption of 20 CFM per occupant.
>>
>>To us, both of these methods seem to be accepted modeling practice for
>>determining measure performance. However, as stated pretty explicitly in
>>the archived credit interpretation requests (CIRs) on the LEED site, LEED
>>won't allow for the adjustment of schedules to simulate these
>>measures. Does anyone have a method (or insight into developing a
>>method) for either of these calculations in a manner that would be
>>acceptable for the LEED process?
>>
>>Many thanks in advance for your responses.
>>
>>Wade
>>
>>Wade McLaughlin
>>DMI
>>450 Lexington St.
>>Newton, MA 02466
>>p 617-527-1525 x103
>>f 617-527-6606
>>
>>
>>
>>
>>
>>
>>You received this e-mail because you are subscribed
>>
>>to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
>>
>>from this mailing list send a blank message to
>>
>>BLDG-SIM-UNSUBSCRIBE at GARD.COM
>Marcus B. Sheffer energy & environmental consulting
>Energy Opportunities 717-292-2636
>1200 E Camping Area Road Fax: 717-292-0585
>Wellsville, PA USA 17365-9783 sheffer at sevengroup.com
>a Seven Group member company www.sevengroup.com
Marcus B. Sheffer energy & environmental consulting
Energy Opportunities 717-292-2636
1200 E Camping Area Road Fax: 717-292-0585
Wellsville, PA USA 17365-9783 sheffer at sevengroup.com
a Seven Group member company www.sevengroup.com
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20030602/886d1296/attachment-0002.htm>
More information about the Bldg-sim
mailing list