[BLDG-SIM] Calibrated models
Carlos Lisboa
carloslx at mail.telepac.pt
Thu Mar 13 03:00:32 PST 2003
I am a portuguese HVAC designer and consultant and a user o DOE2.1-E for
over ten years. Usually I use DOE for new buildings, but five years ago
I participated in an Energy Audit of six buildings in Portugal and had
my first and only experience of DOE model calibration. I used the
folowing methodology (work done with the colaboration of an electricall
engineer):
1.Preparation of building inspections (average 2 days work).
-study of building and systems drawings and specifications,
-study of energy monthly bills,
-conception and organization of forms to be filled in the building
inspection work,
2.Building inspection (average 2 days work).
This included;
-filling a form for each room in the building, in wich all the
relevant
aspects where characterized (lighting, equipment, hvac equipment,
people, schedules).
-characterization of the HVAC systems installed
-characterization of other energy consuming equipment installed
(elevators, water and sewage pumps, exterior lighting, etc.)
-interview with people responsible for building operations to
determine
operating schedules and the way the building systems were operated
3.Field Measurements (average two weeks)
This included;
-total building energy consumption during one week registered with
a
portable electricall energy analiser (output to a PC),
-registration of energy consumption of speciall energy consumers
(elevators, computer rooms, plugs and lighting in office
floors, etc.)
-measurement of power consumption of speciall equipments (water and
sewage pumps, lighting, etc.)
-measurement of main airflows and hvac effective working
conditions,
4.Creation of a DOE model (average 3 days)
This included;
-model in a room by room basis
-including all non HVAC consumers
5.Calibration (hourly) for a week day an weekend measured (average
1day).
This included;
-use of a meteorological day (in the TRY, only available
meteorological data )
similar to the meteorological conditions of the day in wich the
measurements
where taken,
-use of hourly energy use schedules for each zone of the building
for all energy consumers
-calibration against the actual hourly energy measured,
6.Verification of the calibrated model against existing monthly bills
(average 1day)
This included;
-DOE calculation of monthly energy consumption using the
calibrated
model and a TRY year (only available meteorological data)
-comparation of calculated monthly consumptions and the actual
energy
consumption of the existing bills for the last years.
This experience showed the following;
I.The hourly calibration against a day of measured data allowed for a
close match of
not weather dependent energy consumer sectors (equipment, lighting,
escalators,
water and sewage pumps, etc.).
I I. The use of the hourly calibrated model for the monthly energy
calculations (using TRY) showed in all cases an acceptable match with
the existing bills.
I I I. The bigger energy consumers were lighting and equipment, wich are
not weather
dependent and easy to calibrate. HVAC acounted for around 20 to 25% of
the total building energy consumption.
Carlos Lisboa
Carlos Lisboa, Lda
TagusPark, Núcleo Central, 46
2780 920 OEIRAS
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20030313/02f41b60/attachment-0002.htm>
More information about the Bldg-sim
mailing list