[bldg-sim] OA loads

Chris Jones cj at cr-jay.ca
Mon Mar 15 14:40:05 PST 2004


You won't find a report that tells you the actual OA heating and cooling 
loads - sensible and latent.  You need to calculate that yourself based on 
the outdoor air ratio at the peak heating/cooling times.

You can use hourly reports to help with this task.


>Hi:
>Outside ventilation air loads are excluded from the LS-C report in DOE 2. 
>Is it reported in any other report - as it is usually a major % of the 
>total loads. Is it in any of the system reports? Latent / sensible 
>separated, etc
?
>How does one read it in DOE 2?
>Thank you.
>~m
>
>
>
>
>
>
>You received this e-mail because you are subscribed
>to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe
>from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at GARD.COM


Chris Jones, P.Eng.
14 Oneida Avenue
Toronto, ON M5J2E3
Tel. 416 203-7465
Fax. 416 946-1005 

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM



More information about the Bldg-sim mailing list