[BLDG-SIM] Occupancy based ventilation
Varkie Thomas
Varkie.Thomas at som.com
Fri Sep 3 08:53:49 PDT 2004
Here is a possible solution (DOE2.1E) for occupancy based ventilation
using CO2 sensors in the return air system.
Create a MIN-AIR-SCH in the SYSTEMS module that is the occupancy
schedule from the LOADS module multiplied by the ratio of the design OA
and design SA. Is this reasonable?
Example
LOADS
$ OFFICE Section 10 Code of Federal Regulations Part 434 (10CFR434) $
SCH-OFFC-OCC = SCHEDULE THRU DEC 31
(WD) (1,24) = ( 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.10 0.20 0.95 0.95
0.45
0.45 0.95 0.95 0.95 0.95 0.95 0.30 0.10 0.10 0.10 0.00
0.00 )
(SAT) (1,24) = ( 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.10 0.10 0.30 0.30
0.30
0.30 0.10 0.10 0.10 0.10 0.10 0.00 0.00 0.00 0.00 0.00
0.00 )
(WEH) (1,24) = ( 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00
0.00
0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00
0.00 )
..
SYSTEMS
$ Occupancy based Ventilation Control = Occup-Profile * OA/SA. OA/SA =
0.20 $
SCH-OCCP-VNT = SCHEDULE THRU DEC 31
(WD) (1,24) = ( 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.02 0.04 0.19 0.19
0.09
0.09 0.19 0.19 0.19 0.19 0.19 0.06 0.02 0.02 0.02 0.00
0.00 )
(SAT) (1,24) = ( 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.02 0.02 0.06 0.06
0.06
0.06 0.02 0.02 0.02 0.02 0.02 0.00 0.00 0.00 0.00 0.00
0.00 )
(WEH) (1,24) = ( 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00
0.00
0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00 0.00
0.00 )
..
AHU-3-6 = SYSTEM
SYSTEM-TYPE = VAVS
Etc.
MIN-AIR-SCH = SCH-OCCP-VNT $ Occupancy based
ventilation $
Etc.
..
Varkie Thomas
SOM
-----------------------------------------------------------
-----Original Message-----
From: postman at gard.com [mailto:postman at gard.com] On Behalf Of Jeff
Hirsch
Sent: Friday, September 03, 2004 9:19 AM
To: BLDG-SIM at GARD.COM
Cc: geraldpde at yahoo.com
Subject: [BLDG-SIM] eQUEST: Bypass damper for Heat Recovery
DOE-2.2, and thus eQUEST, does not currently have models of CO2 sensors
and controls but does model many types or heat recovery; look in the
DOE-2.2 Dictionary (Volume 2) on page 344-358 (PDF page 346-360) for the
details of keywords that are used to define the Energy Recover
Ventilator (ERV)
capabilities. Links to the six volumes of DOE-2.2 documentation for
eQUEST
are found below the program download links (for the standard and
refrigeration
system version of eQUEST - currently version 3.51 pre-release) at the
website
http://DOE2.com/eQUEST/
(Direct link to DOE-2.2 command and keyword dictionary in PDF format is
http://doe2.com/download/DOE-22/DOE22Vol2-Dictionary.pdf)
We have a project underway to adds some forms of CO2 sensors and
controls into DOE-2.2; those features may not be available until early
next year. Until that time you would need to use a scheduled minimum
OA damper position to approximate the CO2 controls.
---
Jeff Hirsch
James J. Hirsch & Associates
Building Performance Analysis Software & Consulting
12185 Presilla Road
Camarillo, CA 93012-9243 USA
phone: (805) 553-9000
fax: (805) 532-2401
email: Jeff.Hirsch at DOE2.com
web: http://DOE2.com
----- Original Message -----
From: "Gerald Pde" <geraldpde at yahoo.com>
To: <BLDG-SIM at GARD.COM>
Sent: Friday, September 03, 2004 6:18 AM
Subject: [BLDG-SIM] eQUEST: Bypass damper for Heat Recovery
> Hi All,
> I am trying to modeling a system in eQUEST with an
> outdside air heat recovery. The unit has a built in
> bypass dampers on the return air to the energy wheel
> and the outside air.The outside air will be reduced by
> use of a CO2 monitor and the bypass dampers on the
> energy recovery wheel, that allows the return air to
> go directly to the coil section.
> 1) What is the method of installing a bypass damper in
> to the heat recovery in equest.
> 2) Is there a method of adding a CO2 meter which would
> regulate the outside to do in directly to the coil?
>
> Thanks,
> Gerald
>
>
>
>
> __________________________________
> Do you Yahoo!?
> New and Improved Yahoo! Mail - 100MB free storage!
> http://promotions.yahoo.com/new_mail
>
> ======================================================
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list