[bldg-sim] eQuest: Two speed AHU
Graham & Megan
hamnmegs at ozemail.com.au
Tue Apr 5 14:12:03 PDT 2005
Pedro,
If the low speed mode is for night cooling only (i.e. full speed during
occupied hours), then you should be able to use the night cycling keywords
(see NIGHT-CYCLE-CTRL). I haven't applied these to a constant volume system
such as SZRH, but I believe these will allow you to simulate your problem.
I would suggest looking carefully at hourly reports to make sure the night
purge is working as you envisaged as overcooling can easily lead to an
unwanted heating load; you can play with seasonal heating setpoints to
overcome some of this ...
Regards,
Graham
----- Original Message -----
From: "Pedro Rodrigo" <pedromanuelrc at yahoo.es>
To: <bldg-sim at gard.com>
Sent: Wednesday, April 06, 2005 1:32 AM
Subject: [bldg-sim] eQuest: Two speed AHU
> Hi all:
> My building has a constant volume AHU with a two speed
> fan, and I'm thinking in using the low speed for night
> and the high speed for day. I'm not sure how to model
> it in eQuest.
> I've realised that the FAN-CONTROL command has an
> option for "two speed" but it's only allowed for PTAC
> system. My AHU is a two-pipe unit.
> Do you have any suggestions to model this system?
> Thanks in advance,
> Regards,
> Pedro Rodrigo
> University of Jaen, Spain
>
>
>
>
> ______________________________________________
> Renovamos el Correo Yahoo!: ¡250 MB GRATIS!
> Nuevos servicios, más seguridad
> http://correo.yahoo.es
>
> ======================================================
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list