[BLDG-SIM] Heating Load question
Mike Tillou
miket at etcgrp.com
Wed Jun 15 16:10:30 PDT 2005
Vikram,
I am guessing that this is what the problem is.
You need to enter a value for "HEAT-SET-T", something like 95F will
work. The default is "COOL-SET-T" which I am guessing you have set to
~55F which is why you're not getting any heat out of the main heating
coil. To activate the zone level re-heat coils you need to be sure to
specify a reheat delta-T. Both of these keywords are on the main
heating tab of the HVAC System.
Regards,
Mike
Michael Tillou, PE
etc Group, Inc.
PO Box 7, Williamstown, MA 01267
ph. (413) 458-9870 fx. (413) 458-9875
-----Original Message-----
From: postman at gard.com [mailto:postman at gard.com] On Behalf Of Vikram
Sami
Sent: Wednesday, June 15, 2005 5:01 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Heating Load question
I'm trying to model a packaged VAV system in eQUEST (v5.2), and I find
that I am not getting a heating load. I have the heating setup as hot
water coils. When I model the system as packaged multizone I get a
heating load, but this disappears when I use the packaged VAV option. Is
there a setting I need to turn on? Or is this simply not an option with
eQUEST?
Thanks
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
Responsive Design * Technological Expertise * Exceptional Service
www.lordaecksargent.com
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20050615/f32fd284/attachment-0002.htm>
More information about the Bldg-sim
mailing list