[BLDG-SIM] Garage Heating
Jeff Haberl
jeffhaberl at tees.tamus.edu
Fri May 13 13:42:04 PDT 2005
Check with Prof Rick Strand at the Univiversity of Illinois.
Jeff
BB 8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) :=') 8=) 8=) 8=? BB
Jeff S. Haberl, Ph.D., P.E.............................jhaberl at esl.tamu.edu
Professor......................................................Office Ph: 979-845-6507
Department of Architecture.......................Lab Ph: 979-845-6065
Energy Systems Laboratory.......................FAX: 979-862-2457
Texas A&M University..............................77843-3581
College Station, Texas, USA.......................URL: www-esl.tamu.edu
BB 8=/ 8=) :=) 8=) ;=) 8=) 8=() 8=) 8=? 8=) 8=) 8= BB
-----Original Message-----
From: postman at gard.com <postman at gard.com>
To: BLDG-SIM at gard.com <BLDG-SIM at gard.com>
Sent: Fri May 13 13:38:57 2005
Subject: [BLDG-SIM] Garage Heating
All;
I simulated an existing 5-bay garage and attached 2000 sf offices in
Colorado, and calibrated a DOE-2 model with real weather and bills.
Infiltration must be about 65% of the annual building heat load, even
with fairly bad walls. The owner wants to build another one with minor
changes. The garage is heated with overhead low-intensity tube heaters
with a combined output of 200 Btuh/sf. The high capacity can also handle
some ventilation, if anyone ever turned it on. When it is cold and the
doors are opened the thermostats will kick all these heaters on. With
bay doors on each side, the room is probably over 100 ac/hr for an hour
per day and there are a few more hours with just one door open,
depending on occupant behavior.
I notice that radiant hydronic in-floor heat is installed in repair
garages at 35 Btuh/sf at design conditions, much lower than my system.
It would seem the heat rate off the floor could increase momentarily
when a draft of cold air hits a warm floor, but is limited over time to
the much smaller boiler capacity. So is some of the claimed savings from
in-floor heat in these types of spaces just from less "recovery
capacity," and less output during periods of extreme airflow. I suppose
I could "simulate" this by merely reducing the capacity while leaving
the infiltration schedule the same, and I would just show more hours
with loads not met. My old standby DOE-2 has limitations for this type
of situation obviously. These peak infiltration events are subhourly; my
workaround is to group them into an hour, and the calibration to monthly
bills is actually quite good.
Does anyone know of comparisons between similar buildings with these two
types of "radiant" heat, or have experiences with actual installations,
or other programs. The setpoint is already down at 60F so I'm not going
to "simulate" one system as better than another by changing the setpoint
down.
--
Fred W. Porter