Yes, you can model ground source heat pump systems (GSHP). How accurate the
results are I'm not sure. You have to create a Loop in water side and then
add a Ground Loop Heat Exchanger. Check the min and max alarm temperatures
since sometimes these need to be adjusted.
I did model a small 10,000 sf building a few years ago in eQuest with GSHP
and compared it to actual data. Predicted was 43 kBtu/sf/yr and actual was
25 kBtu/sf/yr (a 99 Energy Star rating!) My life cycle cost results showed
the indirect/direct evaporative cooling was better than GSHP (since the
building was in a dry climate of Colorado), however the owner wanted to go
with the GSHP system. The owner is very energy conscious so they do turn off
equipment at around 3 PM for this school maintenance building which might be
part of the low energy usage, however, I wonder if eQuest under-predicts the
savings from GSHP systems?
GSHPs are all the rage, but I don't think they are cost-effective if you
have natural gas for heating as your base case. But then again, with the
rising cost of natural gas, maybe they will be more affordable. Anyone else
have any experience with predicted versus actual energy performance for GSHP
systems?
Renee
-----Original Message-----
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Leela Kala
Sent: Friday, September 30, 2005 9:17 AM
To: bldg-sim at gard.com
Subject: [bldg-sim] GHP in eQuest
Hi,
Can I model GHP in eQuest? If yes, I will appreaciate
if someone can send me teh details.
thanks
Leela
__________________________________________________________
Yahoo! India Matrimony: Find your partner now. Go to http://yahoo.shaadi.com
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list