Dear Scott:
Without looking at your model inputs, I wonder if your model may be in a heating dominated climate.
Overhangs can reduce your cooling load, but the heating load may be increased as a result of the added shading during winter.
If the heating load increase overshadows the cooling load savings from that measure, the net energy consumption may increase.
I hope this helps.
Sean
Sean Henry, LEED® AP | Energy Specialist
INTERFACE ENGINEERING
708 SW Third Avenue | Suite 400 | Portland, OR 97204
________________________________________
From: BLDG-SIM at GARD.COM [mailto:BLDG-SIM at GARD.COM] On Behalf Of Scott Runyon
Sent: Thursday, April 27, 2006 11:03 AM
To: BLDG-SIM at GARD.COM
Subject: [BLDG-SIM] Explain this: overhangs in eQuest
Explain this:
How can I add overhangs to my South Facing windows and my electric and gas consumption go up for the year?
I thought I was adding these to conserve energy!
I have done this on a simple generic building and the same result happened.
Any help would be appreciated.