Brad,
Here are my understandings.
1. Qualified computer software for purpose of Energy Efficient
Commercial Building Tax Deduction under IRS Code 179D are four (4):
a. Trace 700
b. Energy Plus
c. HAP
d. Visual DOE
The e-Quest is not on the list.
2. My reading to IRS notice 2006-052 is that, either to achieve
total 50% saving to get $1.80/sf, or to achieve 16-2/3% individually for
each subject of the three to get $0.60/sf for each subject. This is a
clear-cut deal, and does not count for partial credit if total below
50%.
Regards,
Shawn Lee
Beardsley Design Associates
Auburn, NY
________________________________
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Brad
Bergler
Sent: Thursday, December 28, 2006 6:49 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] E-pact 2005 energy incentive questions
Two energy incentive questions for the group:
1. Does anyone know the status of eQuest with regard to it's
listing by the DOE as approved software for compliance with the 2005
e-pact energy tax incentives?
2. With respect to "partially qualifying property" section 2
paragraph .03 of IRS notice 2006-052. Does anyone have an opinion as to
the intent of breaking the "property" into three components; Envelope,
HVAC, and Lighting? If a building cannot beat 90.1-2001 by 50%, must the
budget building be modeled against the same building with only the
lighting changed, and beat 90.1 by 16.7% in order to achieve partial
credit of $0.60/SF? Or can the proposed building with all ECM's be
modeled against the budget building and achieve partial credit? If the
intent of E-pact is to encourage energy efficient buildings, it seams
that save 20% and 30% over 90.1 would be eligible for partial credit.
Thanks for your input,
Brad
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20061229/9a1b4f3d/attachment-0002.htm>
More information about the Bldg-sim
mailing list