[bldg-sim] CW Loop Ctrls
Brian Fountain
bfountain at greensim.com
Wed Feb 15 10:26:21 PST 2006
On the first question, one of the chiller types in eQUEST is "water
economizer" - which is effectively a heat exchanger between the
chilled and condenser water loops. You will have to play with your
loop equipment controls and load management to set when the chillers
are cooling and when you are on "free cooling".
Brian Fountain
GreenSim
-----Original Message-----
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of
Sarathy Narasimhan
Sent: February 15, 2006 12:50 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] CW Loop Ctrls
I was simulating the central plant for a hotel in eQuest. I have a
couple of questions on modeling the condenser water control.
1. I was trying to model free-cooling plate-to-frame heat
exchanger between CW & CHW loops - eQuest 3.55 doesn't seem to handle
this. Any suggestions?
2. When I tried to add VFD on my condenser water pumps, I get a
bunch of warnings as shown below. I haven't used any custom curves for
the pumps (though I used them for the chillers being modeled - but I
tried changing them to default and even then the warnings wouldn't go
- not sure exactly what they mean - any help would be greatly
appreciated)
CURINV: No real root for CURVE:
1 1.353483 0.015932 -0.369414 0.000000 0.000000 0.000000
Thank you,
Sarathy Narasimhan
Analyst, Energy Efficiency
Energy and Power Solutions, Inc.
<http://maps.yahoo.com/py/maps.py?Pyt=Tmap&addr=150+Paularino+Avenue&c
sz=Costa+Mesa%2C+CA+92626&country=us> 150 Paularino Avenue Suite A120
Costa Mesa, CA 92626
<mailto:sarathyn at energynpower.com> sarathyn at energynpower.com
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20060215/3a91c245/attachment-0002.htm>
More information about the Bldg-sim
mailing list