[BLDG-SIM] About thermostatic valves in zone equipment

answers at healthyheating.com answers at healthyheating.com
Fri Mar 3 07:28:49 PST 2006


Pedro,

If your coils are based on a 20 deg F delta T with 180 deg F fluid
supply temperatures ( variable flow constant temp) you will need valves
with inverse characteristics to the fan/coil (i.e. Logrithmic (eq%) or
modified splits)... constant flow variable temp systems tend to behave
more linear...i.e. 50 flow delivers 50% output.
Ref.: Total Hydronic Balancing, Prof. Robert Petijean.

Best Regards,

Robert Bean, R.E.T.
Registered Engineering Technologist
Professional Services
Corporate Development and Building Technologies

Home of the Carlson – Holohan Industry Award of Excellence
 
Tel.: 403.255.0121
Cell: 403.560.5769
Email: info at healthyheating.com
http://www.healthyheating.com/ 
 
 
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Pedro
Rodrigo
Sent: Friday, March 03, 2006 1:36 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] About thermostatic valves in zone equipment

Hi all:
We´re modelling a building with a number of
water-to-air fancoils in each thermal zone.
We have yet built the coils without problems.
However we are not sure about the valves that control
water flow rate. We think that processes such us
histeresis, uncertainties in actuator position or
relation between position and water flow should be
taken into account.
We have lacks of references and documentation about
this.
Do you know something interesting to read about the
matter?
Thanks in advance,
Regards,

Pedro Manuel Rodrigo Cruz
University of Jaen, Spain


		
______________________________________________ 
LLama Gratis a cualquier PC del Mundo. 
Llamadas a fijos y móviles desde 1 céntimo por minuto. 
http://es.voice.yahoo.com

======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM



===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM



More information about the Bldg-sim mailing list