[BLDG-SIM] Chilled Beams and eQUEST
Timothy Moore
tcm at berkeley.edu
Wed Apr 25 16:41:37 PDT 2007
Ryan,
If the chilled beams are in fact active, these approaches may work well,
since they are essentially terminal cooling coils with no terminal fan. IF
you are interested in optimizing performance related to thermal comfort,
however, you'll need to seek other tools, since eQuest is obviously not
explicitly accounting for the radiant cooling effect that chilled beams
include to one degree or another.
Also, if you are considering passive chilled beams (radiant panels with fins
or slots to increase convective cooling, but no direct coupling to
mechanically driven supply airflow), you'll need to be sure to account for
the appropriate cooling capacity given the anticipated beam-to-air delta-T
for the application and no mechanically driven airflow.
FYI: There are plans afoot and some groundwork laid to create a radiant
cooling model within eQuest. Pending funding (presently the significant
unknown, but watch this space), the idea will be to include a simple radiant
cooling terminal unit that can be used with any of the airside systems (much
the way baseboard heaters can be added in version 3.6). While the details
are far from being hammered out, it is possible that this could include
means of adjusting for the degree of convective interaction with room air,
air passively drawn from the return plenum (as would be the case for the
"chilled sails" from Price when used in a T-bar grid with DOAS), or SA from
a central air handler.
Best of luck,
Timothy Moore
Integrated Sustainable Design Consultant
LEED AP
Whole Systems Design
910 Indian Rock Ave.
Berkeley, CA 94707
Ph: (510) 525-4809
Fx: (413) 480-7252
Mobile: (303) 324-1044
tmoore at whole-systems-design.com
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Ryan Hammond
Sent: Wednesday, April 25, 2007 1:55 PM
To: BLDG-SIM at gard.com
Cc: Nathan Fleischer
Subject: [BLDG-SIM] Chilled Beams and eQUEST
Thanks Gerald for this.
R. Ryan Hammond, LEED(r) AP
Designer
G U T T M A N N & B L A E V O E T
C o n s u l t i n g E n g i n e e r s
2351 Powell Street 1111 Howe Ave., Suite 155
San Francisco, CA 94133 Sacramento, CA 95825
P (415) 625-0730 P (916) 921-1981
F (415) 625-0735 F (916) 921-1921
E RHammond at gb-eng.com
W www.gb-eng.com
-----Original Message-----
From: Gerald Pde [mailto:geraldpde at yahoo.com]
Sent: Wednesday, April 25, 2007 1:53 PM
To: Ryan Hammond; BLDG-SIM at gard.com
Cc: Nathan Fleischer
Subject: Re: [BLDG-SIM] Chilled Beams and eQUEST
You can use induction units to simulate a chilled beam system but you might
also need to configure a seperate (or secondary) warmer chilled-water loop
and cooler hot-water loop for the zonal coils. You might also need to check
the induced ratio to scale the capacity of the primary air delivery and the
secondary induced air component.
Hope this helps.
Gerald
--- Ryan Hammond <RHammond at gb-eng.com> wrote:
> All,
>
>
>
> Has anyone out there had experience modeling chilled beams with
> eQUEST?
>
>
>
>
> How's it done?
>
>
>
> Thanks,
>
> R. Ryan Hammond, LEED(r) AP
>
> Designer
>
>
>
> G U T T M A N N & B L A E V O E T
>
> C o n s u l t i n g E n g i n e e r s
>
>
>
> 2351 Powell Street 1111 Howe Ave.,
> Suite 155
>
> San Francisco, CA 94133 Sacramento, CA 95825
>
> P (415) 625-0730 P (916)
> 921-1981
>
> F (415) 625-0735 F (916)
> 921-1921
>
> E RHammond at gb-eng.com
>
> W www.gb-eng.com
>
>
>
>
>
>
=====================================================You
> received this e-mail because you are subscribed to the
> BLDG-SIM at GARD.COM mailing list. To unsubscribe from this mailing list
> send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM
__________________________________________________
Do You Yahoo!?
Tired of spam? Yahoo! Mail has the best spam protection around
http://mail.yahoo.com
==================
You received this e-mail because you are subscribed to the BLDG-SIM at GARD.COM
mailing list. To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list