[BLDG-SIM] Equest - Modeling a radiant floor heating system and a seperate cooling system
Peter Alspach
peter.alspach at arup.com
Thu Apr 19 17:24:04 PDT 2007
Sharon - you can't do this without some serious "faking" within eQuest -
only one system per zone. However, if you treat your radiant floor as
baseboard heaters (basically just BTU injectors) then you can combine
your "radiant floor" with cooling ventilation units, such as a VAV
system. always worth double checking that it is working correctly
though.
peter
________________________________
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Sharon
Gould
Sent: Thursday, April 19, 2007 12:52 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Equest - Modeling a radiant floor heating system and
a seperate cooling system
How does one model two isolated HVAC systems serving one zone?
I have a mixed use building with radiant floor heating (lots of
concrete) with a completely separate air side cooling system. There is
a potential of running the ventilation loads through an ERV.
Sharon Gould, P.E., LEED(r) AP, CEM
Franklin Energy/Focus on Energy
Apartment and Condo Efficiency Services
211 S. Paterson Street, Suite 200
Madison, WI 53703
Ph: 608-310-6910/888-201-4061
Fax: 608-310-6909
Email: sgould at franklinenergy.com
Visit our website at: www.focusonenergy.com
<http://www.focusonenergy.com/>
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070419/aef47376/attachment-0002.htm>
More information about the Bldg-sim
mailing list