[bldg-sim] Modeling buildings with natural ventilation forAppendix G

Gerald Pde geraldpde at yahoo.com
Wed Feb 7 12:38:38 PST 2007


Following up with these discussions, I wonder if this
would this be an acceptable way to estimate natural
ventilation in Appendix-G,

1) I first determine the hourly values for dry bulb,
humidity ratio and wind speed of the location of my
project. 

2) Secondly, I assume certain environmental/comfort
criteria that would be conducive to naturally
ventilate. In my case I assumed a temperature range of
55 F to 75 F ;a humidity ratio range of 48 Grains to
85 Grains; and wind speed between 1 to 15 m/sec. Thus
bracketing a temperature range between 55 and 75 and
limiting relative humidity to 60%. For these ranges, I
can naturally ventilate and hence the HVAC equipment
can be shut down. Also since these conditions are
evaluated hourly, I assumed a time buffer where the
building occupants take a slightly longer response
time if the conditions drift from the comfort range.

3) I evaluate these conditions hourly and flaged (1 or
0) each and every hour when these conditions are met.

4) Finally, I then took an hourly output of fan energy
from DOE-2 hourly report and match them up with the
natural ventilation FLAG and then calculate the total
fan energy reduction when the HVAC system is shut off
when the NV conditions are met. These results can be
then averaged out annually. 

The fan power reductions in % can also be translated
in terms heating energy reductions during the winter
time but it was not significant for the location I was
simulating for. I found the greatest fan energy saving
to be during the shoulder periods of April, May and
October. In total, it was about a 9% total HVAC (fans,
pumps and heating and cooling) energy reductions and a
14% fan energy reduction which was not a huge amount
when it came to total energy reductions and factoring 
all end use components.

Let me know if anyone has any thoughts or comments and
critically if this is an acceptable way to estimate NV
savings in Appendix-G.

Thanks.
Gerald



--- Michael Rosenberg <Michael.Rosenberg at state.or.us>
wrote:

> That makes sense to me. You might get a little
> additional savings due to
> the fact that you are not adding heat from the fan
> to the airstream with
> natural ventilation, as you would with an
> economizer. 
> 
> Mike
> 
> Michael Rosenberg
> Oregon Department of Energy
> 625 Marion St. N.E.
> Salem, OR 97301-3742
> Phone : (503) 373-7809
> Fax: (503) 373-7806
> 
> >>> "Jon McHugh" <Jon.McHugh at h-m-g.com> 12/21/06
> 03:33PM >>>
> Michael,
> 
> From the sound of this natural ventilation would
> only save fan energy
> as
> compared to an air conditioner that has an
> economizer, is this
> correct?
> There would not be any additional compressor
> savings, is this correct?
> 
> Thanks,
> 
> Jon McHugh
> 
>  
> 
> -----Original Message-----
> From: bldg-sim at gard.com [mailto:bldg-sim at gard.com]
> On Behalf Of
> Michael
> Rosenberg
> Sent: Thursday, December 21, 2006 1:03 PM
> To: bldg-sim at gard.com 
> Subject: [bldg-sim] Modeling buildings with natural
> ventilation
> forAppendix G
> 
> Marcus,
> 
> I am on the ASHRAE 90.1 ECB subcommittee. I do not
> think at this point
> that we are working on any additional methodology to
> credit natural
> ventilation. Addendum AG already changed the
> following:
> 
> In the proposed building.
> HVAC Fan Schedules. Schedules for HVAC fans that
> provide outdoor air
> for
> ventilation shall run continuously whenever spaces
> are occupied and
> shall be cycled on and off to meet heating and
> cooling loads during
> unoccupied hours. 
> 
> This implies that HVAC fans that are only meeting
> thermal load may
> cycle
> on and off, and was meant to allow fan credit for
> natural ventilation
> system (as simple as operable windows). The proposed
> building still
> calls for cooling as a requirement, but the thought
> is, that if model
> simulates natural ventilation and the cooling load
> is met that way,
> the
> fan and cooling coil will not operate to meet load
> and the design will
> be credited. The problem is that most LEED models
> are done using DOE2,
> which has severe limitations when it comes to
> modeling natural
> ventilation. It is my understanding that other
> programs do a better
> job
> of this.  
> 
> The subcommittee also thought that an exceptional
> calculation method
> might be used if the natural ventilation simulation
> was be done in a
> stand alone program and then an appropriate
> infiltration schedule was
> input into a program like DOE2, reducing the use of
> mechanical
> cooling.
> 
> 
> Mike
> 
> 
> 
> Michael Rosenberg
> Oregon Department of Energy
> 625 Marion St. N.E.
> Salem, OR 97301-3742
> Phone : (503) 373-7809
> Fax: (503) 373-7806
> 
> >>> "Marcus Sheffer" <sheffer at sevengroup.com>
> 12/21/06 11:58AM >>>
> Mike,
> 
>  
> 
> The exception calculation method you describe is
> absolutely correct.
> 
>  
> 
> Obtaining savings for natural ventilation within
> LEED however is
> another
> story.  I am one of the certification reviewers and
> also vice-chair of
> the EA TAG.  My understanding is that to date the
> USGBC has not
> allowed
> natural ventilation to fully count under EAc1 even
> if submitted as an
> exceptional calculation method.  The TAG is awaiting
> the work of the
> 90.1 subcommittee you mention to develop a uniform
> methodology.
> 
>  
> 
> Perhaps your submission will be the one to set the
> precedent.  Thanks
> to
> all for helping to blaze the trail. 
> 
>  
> 
> Marcus Sheffer
> 
> Energy Opportunities, Inc/a 7group Company
> 
> 1200 E Camping Area Road, Wellsville, PA  17365
> 
> 717-292-2636,  <mailto:sheffer at sevengroup.com>
> sheffer at sevengroup.com 
> 
> www.sevengroup.com 
> 
>  
> 
>   _____  
> 
> From: bldg-sim at gard.com [mailto:bldg-sim at gard.com]
> On Behalf Of Mike
> Tillou
> Sent: Thursday, December 21, 2006 2:03 PM
> To: bldg-sim at gard.com 
> Subject: [bldg-sim] Modeling buildings with natural
> ventilation for
> Appendix G
> 
>  
> 
> Not yet...I have a project with natural ventilation
> using this method
> that will be submitted for final review in Feb-Mar
> 2007.  
> 
>  
> 
> MMT
> 
> Michael Tillou, PE
> ETC Group, Inc - Energy Engineering for a
> Sustainable Future
> Ph:413-458-9870 
> 
> -----Original Message-----
> From: bldg-sim at gard.com [mailto:bldg-sim at gard.com]
> On Behalf Of Peter
> Alspach
> Sent: Tuesday, December 19, 2006 1:34 PM
> To: bldg-sim at gard.com 
> Subject: [bldg-sim] Modeling buildings with natural
> ventilation for
> Appendix G
> 
> Mike,
> 
>  
> 
> Have you succeeded in getting a naturally ventilated
> building through
> the USGBC with this method?
> 
>  
> 
> If so, I am sure all would be glad to hear it.
> 
>  
> 
> Peter
> 
>  
> 
> 
>   _____  
> 
> 
> From: bldg-sim at gard.com [mailto:bldg-sim at gard.com]
> On Behalf Of Mike
> Tillou
> Sent: Tuesday, December 19, 2006 7:18 AM
> To: bldg-sim at gard.com 
> Subject: [bldg-sim] Modeling buildings with natural
> ventilation for
> Appendix G
> 
> Ramana,
> 
>  
> 
> The ASHRAE 90.1 ECB sub-committee is working on a
> methodology for
> simulating natural ventilation within the framework
> of Appendix G but
> I
> don't think its finished yet.  In the meantime here
> is what I would
> recommend.
> 
>  
> 
> Appendix G / 90.1 ECB allows you to use an exception
> calculation
> method
> to simulate hybrid systems or unique efficiency
> measures to
> demonstrate
> above-standard performance.  I think this would
> certainly apply in
> your
> case.   
> 
>  
> 
> Here's what I have done on projects requiring an
> exception calculation
> method.  
> 
> 1. Establish your energy cost budget and your design
> energy case
> following the Appendix G guidelines.  
> 
> 2. Create a second model using the Design Energy
> Case as the baseline
> and make the necessary modifications to simulate
> radiant heating / no
> cooling via natural ventilation.  
> 
> 3. Report the energy savings from your exception
> calculation as a line
> item at the end of your LEED EA-1 summary table
> (similar to how
> renewable energy is reported). 
> 
> 4.  Include a seperate summary table  for the
> exception calculation
> showing the energy end-use breakdown and how you
> arrived at the cost
> savings. 
> Show
> both the baseline and proposed energy use.  
> 
> 5. Make sure the savings are reasonable and prudent
> for the system you
> are proposing.  
> 
> 6. Document any changes to the model especially
> changes to schedules
> that were necessary to properly simulate your
> system. 
> 
> 7. Make it easy for someone to review your
> assumptions and the
> methodology you used to estimate the savings
> 
>  
> 
> I hope this helps.  Good luck.
> 
>  
> 
> Mike
> 
>  
> 
> Michael Tillou, PE
> ETC Group, Inc - Energy Engineering for a
> Sustainable Future
> Ph:413-458-9870 
> 
> -----Original Message-----
> From: bldg-sim at gard.com [mailto:bldg-sim at gard.com]
> On Behalf Of Ramana
> Koti
> Sent: Monday, December 18, 2006 4:53 PM
> To: bldg-sim at gard.com 
> Subject: [bldg-sim] Modeling buildings with natural
> ventilation for
> Appendix G
> 
> Dear all,
> 
> Is ignoring natural ventilation in both proposed and
> baseline designs
> an
> accepted/fair way of modeling based on Appendix G
> (ASHRAE 90.1-2004)?
> 
> Part of the proposed design has (radiant heating +
> natural
> ventilation)
> with no cooling which was modeled as a radiant slab,
> no cooling,
> natural
> ventilation ignored. 
> 
> But the Baseline HVAC system based on Appendix G is
> System 5: Packaged
> VAV w/Reheat. (Natural ventilation can be modeled
> based on Air Change
> method or Sherman Grimsrud method though I do not
> know how to do it).
> 
> I cannot decide how to make the baseline and
> proposed comparable with
> respect to Natural Ventilation (in a manner
> acceptable to LEED
> review),
> suggestions will be appreciated.
> 
> Thanks,
> 
> Ramana Koti, Sustainable Building Analyst LEED AP
> 
> ELEMENTS | a division of berkebile nelson immenschuh
> mcdowell
> architects
> 106 W. 14th Street Suite 200
> Kansas City, Missouri 64105
> 
> p 816.783.1635 f 816.783.1501
> www.bnim.com| elements.bnim.com
> 
> ==================
> You received this e-mail because you are subscribed
> to the
> BLDG-SIM at GARD.COM mailing list.  To unsubscribe from
> this mailing list
> send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM 
>
____________________________________________________________
> Electronic mail messages entering and leaving Arup 
> business systems
> are
> scanned for acceptability of content and viruses
>  
> ==================
> You received this e-mail because you are subscribed
> to the
> BLDG-SIM at GARD.COM mailing list.  To unsubscribe from
> this mailing list
> send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM 
> 
>  
>  
> ==================
> You received this e-mail because you are subscribed
> to the
> BLDG-SIM at GARD.COM mailing list.  To unsubscribe from
> this mailing list
> send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM 
> 
> 
>
======================================================
> You received this e-mail because you are subscribed
> to the
> BLDG-SIM at GARD.COM mailing list.  To unsubscribe from
> this mailing list
> send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM 
> 
>
======================================================
> You received this e-mail because you are subscribed
> to the
> BLDG-SIM at GARD.COM mailing list.  To unsubscribe from
> this mailing list
> send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM 
> 
> 
>
======================================================
> You received this e-mail because you are subscribed 
> to the BLDG-SIM at GARD.COM mailing list.  To
> unsubscribe 
> from this mailing list send a blank message to 
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
> 
> 



 
____________________________________________________________________________________
The fish are biting. 
Get more visitors on your site using Yahoo! Search Marketing.
http://searchmarketing.yahoo.com/arp/sponsoredsearch_v2.php

======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM




More information about the Bldg-sim mailing list