[bldg-sim] how much cold air infiltration can I really expect?

Glenn Haynes glenn.haynes at rlw.com
Thu Feb 1 07:32:33 PST 2007


Aaron,

 

It is a fact that infiltration or outside air can dominate the heating
loads in buildings with significant internal heat gains, high mass,
insulated shells and/or good or few windows.  It is always a high
contributor per CFM in cold weather, and IAQ concerns can mandate
significant quantities of ventilation air.  Also, bear in mind that
infiltration is always proportional to wind speed, but it can be reduced
significantly when the building is pressurized with outside air drawn in
through air handlers.

 

If you really need to estimate heat losses due to infiltration, you
should apply a method that accounts for the wind speed.  A problem that
you might encounter, however, is the somewhat random nature of this
variable in the TMY and TMY2 files.  I have found that very high wind
speeds can occur during times of relatively mild temperatures, and can
set the peak heating loads.  These wind speeds are relatively random
compared to the dry bulb temperatures in these files because they were
assigned a much lower weight in the statistical selection of the TMY
monthly data.  You can check the wind speed whenever the peak heating
load is occurring at a strange time, and just disregard this peak, or
you can alter the wind speeds in the TMY file you are using.

 

Temperature data in the TMY files are fairly well behaved because they
typically vary much slower than wind speed.  In a truly average season,
the heating loads will be strongly correlated to temperature, but when
you introduce high wind speeds with significant infiltration effects
into a model, a few high hourly wind speeds can dominate your heating
loads.  This is counter-intuitive, and should not be occurring during an
average weather season (although it can truly occur in any single
weather season).  More often than not, we intend to model typical (or
even average) conditions in a building energy and demand simulation.  If
you do not somehow adjust (chop the extremes, average over time, etc.)
the hourly wind speeds in the "typical" weather file, you can obtain
strange hourly heating results due to infiltration.  My personal
preference is to estimate average wind speeds and average peak speeds,
and alter the TMY file to reflect these averages throughout the typical
year.  This way, the average seasonal energy effects of infiltration are
not altered, and the peak wind speeds are kept in place hourly but
buffered (to reflect more typical values).  You can do this or something
similar using the DOE2 weather utilities and a spreadsheet.

 

This might be more than you asked for, but I hope it will help you or
some other modelers on this list to answer some questions you may still
have regarding the effects of infiltration.

 

Glenn Haynes, PE

Senior Consulting Engineer

RLW Analytics, Inc.

860-346-5001x202

 

________________________________

From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of
Dahlstrom, Aaron
Sent: Wednesday, January 31, 2007 9:29 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] how much cold air infiltration can I really expect?

 

I have noticed that infiltration makes up most of the winter heating
load for several high-bay single-story commercial buildings I'm
modeling. (big-box retailer, light manufacturing facility)

 

I've used a variety of methods - ACH estimates, CFM / so of facade (per
ASHRAE F27.10), and Area(crack) x Velocity(winter wind) - to estimate
infiltration.

 

Have other people stuck with these methods? Or does anyone know of
better ways to estimate infiltration?

 

Aaron Dahlstrom

AKF Engineers, LLP
1500 Walnut Street, Suite 1400
Philadelphia, PA 19102 
Phone:   (215) 282-2169
Fax:        (215) 735-6706
www.akf-engineers.com <http://www.akf-engineers.com/>
 
 _________________

 
CONFIDENTIALITY NOTICE
IMPORTANT: This communication, together with any attachments hereto or links contained herein, is for the sole use of the intended recipient(s) and may contain information that is confidential and/or legally protected and privileged. If you are not the intended recipient, you are hereby notified that any review, redisclosure, copying, dissemination, distribution, forwarding, printing or use of this communication or its attachments is STRICTLY PROHIBITED. If you have received this communication in error, please notify the sender immediately by return e-mail message and delete the original and all copies of the communication, along with any attachments hereto or links herein, from your system. If you disclose this communication to any person or entity without our prior written consent, you may be subject to an action for breach of confidentiality, in addition to all other actions in law and in equity.


===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070201/8227ed53/attachment.htm>


More information about the Bldg-sim mailing list