[bldg-sim] Min Outdoor Air
Aulbach, John
jaulbach at nexant.com
Tue Jan 30 14:15:08 PST 2007
Steve:
What type of HVAC system are you running? A VAV system Outside air will only see the mixing with return air upstream of the coil. The cooling coil will adjust as required to maintain the 55 °F setpoint need as outside conditions change. Downstream, the reheat coils will never see the outside conditions.
Correct me if I am wrong...
________________________________
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Steve Barnell
Sent: Tuesday, January 30, 2007 1:54 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] Min Outdoor Air
Hello,
I am modelling a building in Canada with eQUEST and have several runs varying the min OA rate. In comparing the runs I noticed that the cooling comsumption varied as expected however the Space Heating comsumption is not altered. This seems counter intuitive to me. Any ideas?
-Steve
-- <http://a8-asy.a8ww.net/a8-ads/adftrclick?redirectid=en-mail_a_01>
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070130/a8e6e306/attachment-0002.htm>
More information about the Bldg-sim
mailing list