[BLDG-SIM] Using ASHRAE 90.1 Addenda in LEED projects
David S Eldridge
DSE at grummanbutkus.com
Thu Jul 12 16:05:27 PDT 2007
As another example (since "a" is early in the series) if you chose to
use one of the most recent addenda such as "av", you do not have to use
all of the ones between "a" and "av".
David
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of gail
Sent: Thursday, July 12, 2007 2:39 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] 90.1-2004 Appendix G Glazing for Baseline case
The way it is written (and the way we've been instructed to review it as
USGBC LEED reviewers), you are permitted to apply any of the addenda to
your project. However, for each addendum you choose to apply, the
entire addendum applies, and it applies to any other relevant LEED
points. Paul's example is correct: since both the 25,000 square foot
threshold and the normalized glazing revision are included as part of
addendum a, you would have to follow both of these requirements if you
choose to apply that addendum to the project. However, you are not
required to apply other addenda to the project just because you chose to
follow addendum a.
Best Regards,
Gail Stranske
CTG Energetics, Inc.
On 7/12/07, Michael Tillou <michael.tillou at gmail.com > wrote:
Paul,
My interpretation of the USGBC ruling is the same as yours, I think.
You
cannot pick and choose which items in ASHRAE addenda to use on your LEED
project. You have to choose either 90.1-2004 with no addenda or
90.1-2004
with addenda which would include ALL the published adddenda that apply
to
ALL chapters of 90.1-2004 not just Appendix G. There are currently 42
addenda to ASHRAE 90.1-2004 (a-v,x,y,aa-ae,ag-ar,av...I hope I didn't
miss
any) This decision would also impact your compliance with the EA energy
performance pre-requisite.
As you said "messy".
I think that all the 90.1-2004 addenda will eventually be published as
ASHRAE 90.1-2007 which will simplify keeping track of all the changes.
Regards,
Mike
Michael Tillou, PE, LEED
Tillou Engineering, LLC
Williamstown, MA 01267
P: 413-458-9870 C: 413-652-1087
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Paul
Riemer
Sent: Wednesday, July 11, 2007 4:22 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] 90.1-2004 Appendix G Glazing for Baseline case
Has anyone read the fine print referenced in these strings to reach this
conclusion:
If you are modeling under 90.1-2004 Appendix G for LEED and opt to not
normalize the glazing by orientation under addendum a, then you must
also
except the other portions of addendum a, most notably the revised area
threshold of 25,000 sf for the base HVAC system in Table G3.1.1A.
It seems like a messy and perhaps unintentional convergence of standard
and
policy adoption but it also seems like it is there in black and white.
Any
other conclusions?
Thanks,
Paul Riemer
The Weidt Group
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Michael
Rosenberg
Sent: Wednesday, May 16, 2007 12:47 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] 90.1-2004 Appendix G Glazing for Baseline case
The requirement to distribute fenestration uniformly in horizontal
bands
across the four orientations has been removed from Appendix G in the
published Addenda Supplement to 90.1, 2004. See the ASHRAE website for
the
supplement.
http://www.ashrae.org/technology/page/132
Michael Rosenberg
Oregon Department of Energy
625 Marion St. N.E.
Salem, OR 97301-3742
Phone : (503) 373-7809
Fax: (503) 373-7806
>>> Chris Jones <cj at cr-jay.ca> 5/16/2007 9:56:02 AM >>>
Appendix G notes that for the Baseline building: "Vertical fenestration
areas for new buildings and additions shall equal that in the proposed
design or 40% of gross above grade wall area, whichever is smaller, and
shall be distributed uniformly in horizontal bands across the four
orientations."
Does this mean that the Baseline building gets windows on all walls on
each
orientation whether or not the Design case has a window in all walls on
each
orientation. For example, if the west orientation has 30% glazing
overall
but many spaces have no windows - some walls on the west face have more
that
30%. Do those spaces in the Baseline case get 30% glazing? Or do I
only
put windows in the Baseline case where there are windows in the Design
case.
Thanks for any help!
Chris Jones, P.Eng.
14 Oneida Avenue
Toronto, ON M5J2E3
Tel. 416 203-7465
Fax. 416 946-1005
======================================================
You received this e-mail because you are subscribed to the
BLDG-SIM at GARD.COM
mailing list. To unsubscribe from this mailing list send a blank
message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed to the
BLDG-SIM at GARD.COM
mailing list. To unsubscribe from this mailing list send a blank
message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
------------------------------------------------------------------------
--------
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Leonard
Sciarra
Sent: Tuesday, May 15, 2007 8:52 AM
To: BLDG-SIM at gard.com
Cc: Scott Foster
Subject: [BLDG-SIM] ASHRAE Addendum now allowed for LEED (Major LEED
Decision impacting EAc1 Credit )
FYI,
these are current addenda
Standard 90.1-2004, Energy Standard for Buildings Except Low-Rise
Residential Buildings (I-P and SI versions) The first Addenda Package
includes a, b, c, d, e, f, g, h, i, j, k, l, m, n, o, p, r, s, t, u, v,
x,
and ak Addendum ad is listed separately in the second Addenda package.
Standard 90.1-2004: Addenda Supplement Package (PDF) Standard 90.1-2004:
Addendum ad (PDF) link
http://www.ashrae.org/technology/page/132
Leonard Sciarra, AIA, LEED ap
312.577.6580 (Dir)
G E N S L E R | Architecture & Design Worldwide
30 West Monroe Street
Chicago IL, 60603
312.456.0123
leonard_sciarra at gensler.com
------------------------------------------------------------------------
--------
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Brandon
Nichols
Sent: Monday, May 14, 2007 6:11 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] ASHRAE Addendum now allowed for LEED (Major LEED
Decision impacting EAc1 Credit )
Thanks Gail very much for the notification,
And thanks to whomever was responsible for convincing USGBC to amend the
process. Seems like just a month ago I was railing on about this very
topic; now I'm out of excuses for not drafting up an ASHRAE 90.1
Appendix G
amendment to address shortcomings in the baseline building rotation
exercise.
Regards,
Brandon Nichols, PE
Mechanical
HARGIS ENGINEERS
600 Stewart St
Suite 1000
Seattle, WA 98101
d | 206.436.0400 c | 206.228.8707
o | 206.448.3376 f | 206.448.4450
www.hargis.biz
------------------------------------------------------------------------
--------
From: BLDG-SIM at gard.com [mailto: BLDG-SIM at gard.com] On Behalf Of gail
Sent: Monday, May 14, 2007 3:02 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] ASHRAE Addendum now allowed for LEED (Major LEED
Decision impacting EAc1 Credit )
Dear Fellow Energy modelers,
The following posting has been placed on the USGBC website (
http://www.usgbc.org/ShowFile.aspx?DocumentID=2664 ), which allows the
use of
ASHRAE Addenda for all credits referencing ASHRAE standards.
Use of approved Addenda for ASHRAE Standards referenced in LEED
Background:
ASHRAE currently publishes Continuous Maintenance standards every three
years, with a Supplement published eighteen months after the Standard is
published. In rare cases, addenda are published in between the
eighteen-month periods. LEED development and ASHRAE standards
development
are not aligned and many addenda have been approved that would be useful
for
LEED project teams.
Action:
LEED project teams are required to use the ASHRAE Standard referenced in
the
applicable Reference Guide and are permitted to use addenda within the
most
recent Supplement to that Standard, as well as any approved addenda
published in between the eighteen-month periods. Project teams are
responsible for notifying LEED reviewers of the use of ASHRAE addenda
utilized at the time of project documentation submission.
If a project team elects to use an addendum to an ASHRAE Standard, this
addendum must be applied to the entire LEED submittal.
This should make fenestration modeling much easier for the Baseline Case
for
projects opting to follow the Addendum.
Best Regards,
Gail Stranske
CTG Energetics, Inc.
==================
You received this e-mail because you are subscribed to the
BLDG-SIM at GARD.COM
mailing list. To unsubscribe from this mailing list send a blank
message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
==================
You received this e-mail because you are subscribed to the
BLDG-SIM at GARD.COM
mailing list. To unsubscribe from this mailing list send a blank
message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
==================
You received this e-mail because you are subscribed to the
BLDG-SIM at GARD.COM
mailing list. To unsubscribe from this mailing list send a blank
message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070712/c550ebd1/attachment-0002.htm>
More information about the Bldg-sim
mailing list