[BLDG-SIM] boiler schedule
jimmy jungle
jimmy.jungle at gmail.com
Fri Jul 20 06:50:58 PDT 2007
thanks john,
that was straight to the point and worked great. i had to fiddle
little bit with equipment control tab but got to it.
On 7/19/07, Aulbach, John <jaulbach at nexant.com> wrote:
> Hi Jimmy:
>
> You can use the Equipment Controls and Load Management buttons in the
> lower right hand corner of the Controls Tab under Hot Water Loop under
> Water Side Tab in eQuest (Detailed Edit Mode).
>
> You need to put in a annual schedule (as well as week and day schedule)
> for the boiler sequence you want, by season. You might for example, say
> (for a annual schedule BOILER-SCHED) January thru April is Boiler-Seq-1
> Week-Sch), May thru Sept is Boiler-Seq-2 (Week-Sch), and Boiler Seq-1
> (Week-Sch)for October thru December. Make Boiler-Seq-1 the same Day-Sch
> every day (Mon-Sun+Hol) and the same for Boiler-Seq-2. The Day-Sch for
> Boiler-Seq-1 will have a Flag of 1 every hour of the day (if boiler is
> to be available every hour), and Boiler-Seq-2 and Flag of 2 for every
> hour of the Day-Sch.
>
> The flag is input in the day schedule. The Day-Sch with Flag = 2 will
> have ONLY your summer boiler scheduled. The day-Sch with Flag = 1 will
> have only your winter boiler scheduled. The equipment annual schedule
> will be input in the Qualification Schedule entry on the General Tab of
> the Load management inputs.
>
> Hope this isn't too confusing. All BLDG-SIM members, make sure I said
> this correctly.
>
> -----Original Message-----
> From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of jimmy
> jungle
> Sent: Thursday, July 19, 2007 10:41 AM
> To: BLDG-SIM at gard.com
> Subject: [BLDG-SIM] boiler schedule
>
> hi-
> i'm trying to use 2 different boilers serving same hot water loop at
> different times of the year.
> i couldnt figure out if there's a simple method to schedule such that
> one boiler is on for winter and the other kicks in summer, if needed.
> any help appreciated!
> --
> Jimmy Jungle
>
> ======================================================
> You received this e-mail because you are subscribed to the
> BLDG-SIM at GARD.COM mailing list. To unsubscribe from this mailing list
> send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
>
--
Jimmy Jungle
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list