[BLDG-SIM] eQuest Outside Air Load Report
Michael Tillou
michael.tillou at gmail.com
Tue Jul 24 07:30:19 PDT 2007
Brandon,
I agree that there needs to be better reporting of OA loads in equest. OA
loads only show up in the system reports so you would have to subtract the
building loads from the load reports to get an approximation of the hourly
OA loads. Notice I said approximation. The system reports also include
pipe and duct losses, pump & fan heat and any other system level effects on
your heating/cooling. The best way I have found to check outside air is to
use the hourly reports. Remember you can set the hourly report output to a
format that can be easily opened in Excel if you need to do any additional
calculations.
Mike
Michael Tillou, PE, LEED
P: 413-458-9870 C: 413-652-1087
_____
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Brandon
Nichols
Sent: Monday, July 23, 2007 7:46 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] eQuest Outside Air Load Report
Thanks to all for answers to previous question,
Here's one more... I think it has been asked before although I
Google-scanned the archives could not seem to find it. Namely, where is the
eQuest outside air load reported? I see lots disclaimers for "The above
loads do not include outside air ventilation loads", but no outside air load
ventilation summary.
Do I really have to take a differential between the total load and all other
loads to back-into an outside air load for each space and system? There's
needs to be a better way...!
Thanks in advance,
Brandon Nichols, PE
Mechanical
HARGIS ENGINEERS
600 Stewart Street
Suite 1000
Seattle, WA 98101
www.hargis.biz
d | 206.436.0400 c | 206.228.8707
o | 206.448.3376 f | 206.448.4450
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070724/4b48f705/attachment-0008.htm>
More information about the Bldg-sim
mailing list