[BLDG-SIM] 25% Process Load in ASHRAE baseline building
Marcus Sheffer
sheffer at sevengroup.com
Tue Jun 26 10:10:17 PDT 2007
No need to manipulate the models to get to 25%. It is common for an
elementary school to not have 25%.
If you do not achieve the minimum of 25% all you need to do is submit a
detailed list of the equipment planned for the building to demonstrate
the actual plug load. Be sure to include all loads including cooking,
refrigeration, computers, etc. The last sentence in the third box at
the bottom of page 173 of the LEED v2.2 Reference Guide refers to this
supporting documentation.
Marcus Sheffer
Energy Opportunities, Inc/a 7group Company
1200 E Camping Area Road, Wellsville, PA 17365
717-292-2636, sheffer at sevengroup.com <mailto:sheffer at sevengroup.com>
www.sevengroup.com
________________________________
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Baugher,
Bridgette
Sent: Tuesday, June 26, 2007 11:21 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] 25% Process Load in ASHRAE baseline building
Hello All-
I am using eQUEST to model an elementary school that will be submitted
with the projects LEED documentation. LEED NC 2.2 from October 2005
states that the proposed building "must be compared against a baseline
building that complies with Appendix G to Standard 90.1-2004 (without
amendments). The default process energy cost is 25% of the total energy
cost for the baseline building".
My question: What is the best way to incorporate a 25% process load
into the eQUEST file? I know that I could put in a misc load into the
ASHRAE baseline building I created, and play with that number until it
reaches 25% of the total energy use, but it seems like there should be a
better way to incorporate this load.
Any help is much appreciated!
Thanks,
Bridgette
Bridgette Baugher
2rw Consultants, Inc.
100 10th Street NE
Suite 202
Charlottesville, VA 22902
t) 434.296.2116
f) 434.977.1862
www.2rw.com <http://www.2rw.com/>
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070626/71485d6e/attachment-0008.htm>
More information about the Bldg-sim
mailing list