[BLDG-SIM] Equest: ERU with added heat and vfd's
Brian Fountain
bfountain at greensim.com
Wed Nov 21 08:27:25 PST 2007
The way I would do it is to use the OA-FROM-SYSTEM keyword and add the
ERU as a separate system with ventilation heat recovery. In this way,
you can define the heat recovery and power and flow characteristics of
the ERU explicitly.
I usually do this by first creating a very small (1 sq-ft) dummy
space, then a dummy thermal zone for that space. Then, create the ERU
as a 100% OA constant volume system serving that thermal zone. Now
comes the fun part. You close eQUEST, open the .inp with a text
editor and cut the new system and all its keywords from the bottom of
the list of systems and paste it to the top of the system list. If
you don't do this, when you run the simulation, it will complain that
the OA-FROM-SYSTEM system referenced does not precede the current
system and will abort the sim. Now, reopen eQUEST and in your 6
systems, use the OA-FROM-SYSTEM keyword on the system, OA tab to
define that the ventilation air is coming from your ERU.
Hope this helps.
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Kevin
Kyte
Sent: November 21, 2007 10:55 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Equest: ERU with added heat and vfd's
Simulating an energy recovery unit which serves six air handling
units. I suppose this is simply enough, I split the total cfm into
percentages for each unit and incorporate into each unit's heat
recovery, yes? Is there any way to include additional heat from the
energy recovery unit? Perhaps split the total heat into percentages
and include this in each unit's heating capacity. How about variable
frequency drives on supply and exhaust fans for energy recovery unit?
Perhaps this could be modeled as a 10% reduction in the fan power
similar to occupancy sensors on lights? Regarding LEED, would usgbc
need a credit interpretation request for something like this or maybe
just mentioning it as a default overridden in the submittal would
suffice. Would anyone who has encountered this care to chime in? Any
suggestions would be forthcoming. Thank you.
Kevin Kyte, LEED AP
Jr. Mechanical Engineer
RobsonWoese, Inc.
T: 716-636-1800
F: 716-636-1856
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Zhen
Tian
Sent: Tuesday, November 20, 2007 5:38 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] add ceiling in eQUEST
Dear all,
When I model a one-floor building in eQUEST, I found that adding the
"lay-in acoustic tile" ceiling (no insulation added) will cause the
peak load through roof to zero. When eliminate the ceiling, a large
part of the building heat flow will go through the roof.
I also tried several buildings. When added ceiling, then the heat flow
through roof turns to zero. Does anyone have an idea why this happens?
Thanks a lot.
Regards,
David
_____
Be a better sports nut! Let your teams follow you with Yahoo Mobile.
Try
<http://us.rd.yahoo.com/evt=51731/*http:/mobile.yahoo.com/sports;_ylt=
At9_qDKvtAbMuh1G1SQtBI7ntAcJ%0d%0a> it now.
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20071121/a41e812b/attachment-0002.htm>
More information about the Bldg-sim
mailing list