[BLDG-SIM] Exterior Lighting

Karen Walkerman kwalkerman at gmail.com
Wed Sep 12 06:30:57 PDT 2007


Hi Mark,

In detailed interface, go to "Utility and Economics" and open your Electric
energy meter (EM1).  Under "Direct Loads" you should see a number that
corresponds to the exterior lighting value you entered in the wizard.  There
will also be a schedule associated with it.  This was created from the
"dayshape" entered in the wizard and can be modified, though not as
elegantly as in the wizard.

~Karen~

On 9/11/07, Zoeteman, Mark R. <mrzoeteman at ftch.com> wrote:
>
>  In eQUEST:
>
> How do you change exterior lighting watts in detailed interface that were
> entered in wizard?
> How do you change exterior lighting dayshape in detailed interface that
> gets created from wizard input?
>
> Mark Zoeteman, FTC&H
> 616-464-3739
>
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>


-- 
Karen Walkerman
Second Law Consulting
802-238-0980
kwalkerman at gmail.com


======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070912/256e14de/attachment-0002.htm>


More information about the Bldg-sim mailing list