[BLDG-SIM] Question about Inputting COP and SEER values in Detailed Data Edit Mode

Brian Fountain bfountain at greensim.com
Tue Sep 11 06:57:13 PDT 2007


EIR can definitely be changed in the detailed mode, and also in
parametric runs.

 

COP is converted into "Cooling Electric Input Ratio" or EIR values for
both chillers and for DX cooling.  (See basic chiller screen and
cooling-unitary power screen)

EIR = 1/COP 

EIR = 1/(EER/3.413)

 

____________________________________________

 

-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Jeremy
Plitt
Sent: September 11, 2007 9:25 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Question about Inputting COP and SEER values in
Detailed Data Edit Mode

 

I was wondering if anyone knew how to input COP and SEER values in the
Detailed Data Edit Mode? I am comparing design variations for a
building and am just changing the values from the first file rather
than inputting everything all over again in a new file. Can I change
the COP and SEER values in the Detailed Data Edit Mode or do I have to
go back to the Building Creation Wizard to accomplish this? 

 

Thanks,

 

Jeremy Plitt

Mechanical Engineer

 

Setty & Associates, Ltd.

3040 Williams Drive Suite 600

Fairfax, VA 22031-4618

PH: 703-691-2115 Ext. 123

FX: 703-691-8084

 

 
 
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM


===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070911/af667532/attachment-0002.htm>


More information about the Bldg-sim mailing list