[Bldg-sim] FW: Process fluid cooler simulation using eQuest

Lynn Qualmann LQualmann at sbwConsulting.com
Fri Aug 15 18:12:28 PDT 2008


Thanks for the responses to my industrial fluid cooler question. It
turns out the curves in DOE2 are good for inlet temperatures no greater
than about 90 degF - I would be way out of bounds. A good point was also
made that fouling would probably be a serious matter at those elevated
temperatures. Back to the drawing board... 

 

R. Lynn Qualmann, P.E.

SBW Consulting, Inc.

2820 Northup Way  #230

Bellevue, WA  98004

Phone:  (425) 827-0330

FAX:     (425) 822-8119

e-mail:  rlq at sbwconsulting.com

 

All,

 

I have a need to simulate the performance of a hypothetical fluid cooler
applied to a condenser of a distillation process. I am trying to
determine the energy consumption that is being avoided by the
installation of heat exchangers that are effectively serving the
condensing function. I have data to determine actual hourly values of
heat rejection (BTU/hr), fluid (not water) temperatures and flow rates
and should be able to obtain hourly weather data for the period
corresponding to the data. I can get design values for the fluid cooler
from a vendor. I only need to determine the energy consumed by the fluid
cooler - no other building energy is of interest. I am thinking I may be
able to do this in eQuest, assigning a process load to the fluid cooler
after developing a schedule from the data I have and putting a meter on
the fluid cooler. My concerns are that the fluid is not water (I have
been unsuccessful in the past specifying non-H2O cooling fluids) and
that the temperatures (cooling from 235 degF to 200 degF) may be out of
range for the algorithms. Anyone see any flaws in this approach before I
propose it?

 

Thanks in advance.

 

R. Lynn Qualmann, P.E.

SBW Consulting, Inc.

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080815/46e7ff2a/attachment.htm>


More information about the Bldg-sim mailing list