[Bldg-sim] IES-VE (Nouman Khan)

Nouman nouman310 at yahoo.com
Mon Dec 1 12:43:13 PST 2008


How about using name such as "Visual Environment Energy Modellin" or "Visual Env" so now name is different than the real one.

 
Best Regards;
Nouman Khan




________________________________
From: "bldg-sim-request at lists.onebuilding.org" <bldg-sim-request at lists.onebuilding.org>
To: bldg-sim at lists.onebuilding.org
Sent: Monday, December 1, 2008 3:01:02 PM
Subject: Bldg-sim Digest, Vol 13, Issue 1

Send Bldg-sim mailing list submissions to
    bldg-sim at lists.onebuilding.org

To subscribe or unsubscribe via the World Wide Web, visit
    http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
or, via email, send a message with subject or body 'help' to
    bldg-sim-request at lists.onebuilding.org

You can reach the person managing the list at
    bldg-sim-owner at lists.onebuilding.org

When replying, please edit your Subject line so it is more specific
than "Re: Contents of Bldg-sim digest..."


Today's Topics:

   1. EP-Quick 1.5 Now Available (Jason Glazer)
   2. Appendix G - Base Case Orientations and Glazing
      (Ulrik Welle-Strand Horn)
   3. Performance Rating Method of of Ashrae 90.1 (2004)    Baseline
      Chiller COP (Ho Tinkit)
   4. Re: IES-VE (Jason Glazer)
   5. Re: Appendix G - Base Case Orientations and Glazing
      (James V. Dirkes II  P.E.)
   6. Re: Appendix G - Base Case Orientations and Glazing (Paul Riemer)
   7. Re: Appendix G - Base Case Orientations and Glazing
      (Brenda V. Morawa)
   8. Re: Appendix G - Base Case Orientations and Glazing
      (Ulrik Welle-Strand Horn)
   9. Re: Appendix G - Base Case Orientations and Glazing (Bill Talbert)
  10. Re: Appendix G - Base Case Orientations and Glazing (James Hansen)
  11. Re: Appendix G - Base Case Orientations and Glazing (James Hansen)
  12. Re: calculating the mean monthly outdoor temp (Nathan Miller)
  13. Re: Appendix G - Base Case Orientations and Glazing (Fred Porter)
  14. Re: calculating the mean monthly outdoor temp (JRR)
  15. Re: DOE-2.2 geometry import troubles (Josh K)


----------------------------------------------------------------------

Message: 1
Date: Sun, 30 Nov 2008 18:53:17 -0600
From: Jason Glazer <jglazer at gard.com>
Subject: [Bldg-sim] EP-Quick 1.5 Now Available
To: bldg-sim at onebuilding.org
Message-ID: <4933357D.60303 at gard.com>
Content-Type: text/plain; charset=ISO-8859-1; format=flowed

EP-Quick is now compatible with the revised input language 
of EnergyPlus 3.0. The object names and keywords in the 
latest version of EnergyPlus that changed are now supported. 
You can still use EP-Quick on all of the releases of 
EnergyPlus since version 1.2.1.

EP-Quick is free and available for download from:

http://glazersoftware.com/

Thanks

Jason

-- 
Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair
Admin for onebuilding.org building performance mailing lists


------------------------------

Message: 2
Date: Mon, 1 Dec 2008 17:59:39 +0530
From: "Ulrik Welle-Strand Horn" <ulrik.horn at silpainc.com>
Subject: [Bldg-sim] Appendix G - Base Case Orientations and Glazing
To: "bldg-sim at lists.onebuilding.org" <bldg-sim at lists.onebuilding.org>
Message-ID:
    <343a1a270812010429h497b119cp9578726e07bc10be at mail.gmail.com>
Content-Type: text/plain; charset="iso-8859-1"

Dear all,

When you are rotating the building through 4 different orientations, do you
change the glazing so that the glazing with the highest SHGC is always faces
north, or do you put the glazing with high SHGC on the original north
facade, and then rotate the building so that the high SHGC glazing faces the
east, south and west orientations in subsequent simulations?

Yours faithfully,


*Ulrik Welle-Strand Horn *
Sustainability Engineer

*Silpa Inc.*
*s* i m p l e  .  *s* c i e n t i f i c  .  *s* u s t a i n a b l e
AMERICAS | MIDDLE EAST | ASIA
www.silpainc.com

India: +91.90080.96083
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081201/adefe962/attachment.html>

------------------------------

Message: 3
Date: Mon, 1 Dec 2008 20:43:37 +0800
From: "Ho Tinkit" <ho.tinkit at scottwilson.com.hk>
Subject: [Bldg-sim] Performance Rating Method of of Ashrae 90.1 (2004)
    Baseline Chiller COP
To: <bldg-sim at lists.onebuilding.org>
Message-ID: <D83FD813F91349C98DF04F42F88467FF at hotinkit>
Content-Type: text/plain;    charset="us-ascii"

Regarding to the Performance Rating Method of of Ashrae 90.1 (2004), there
is an issue of  determining baseline Chiller COP need to be clarified.

Regarding to the baseline HVAC system, the parameters need to be set
according to Appendix G of Ashrae 90.1 Standard.
According to table G3.1.1A and table G3.1.1B of App. G3.1.1, the baseline
HVAC system for a building with area larger than 150,000 sqft is specified
as variable air volume with reheat with centrifugal chiller >300tons,
whereas the equipment efficiencies should be modeled at the minimum
efficiency levels in accordance with section 6.4 of Ashrae 90.1 Standard.
Then referring to table 6.8.1 J of section 6.4 of Ashrae 90.1 Standard,
minimum efficiencies for centrifugal chiller COP(standard) should be 6.1.

However, What is the minimum efficiencies for the baseline design COP under
the following condition,
1) If the proposed HVAC design is design to work with leaving chilled water
at 42.8F and entering condenser water temperature of 85F,
2) If the proposed HVAC design is design to work with leaving chilled water
at 42.8F and entering condenser water temperature of 89.6F, and this chiller
is designed to be a ice storage system.

Should the baseline design be modeled at COP 6.1 or should the baseline COP
be estimated by the equations listed below the table 6.8.1 J?

Please advise.

Thanks you for any kindly helps.

Regards,

TK HO
Senior Assistant Engineer
Scott Wilson Ltd
Tel. no. (852) 2410 3847



^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^
Scott Wilson supports the UN Global Compact and Caring for the Climate initiatives.
Please consider the environment and only print this email if necessary. 
^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^
This email and any attachments to it are intended only for the party to 
whom they are addressed. They may contain privileged and / or 
confidential information. If you have received this transmission in error
please notify the sender immediately and delete any digital copies and 
destroy any paper copies. Thank you. Scott Wilson accepts no 
contractual liabilities or commitments arising from this email unless 
subsequently confirmed by fax or letter or as an email attachment 
giving company name, address, registration number and authorized 
signatory.




------------------------------

Message: 4
Date: Mon, 01 Dec 2008 07:19:28 -0600
From: Jason Glazer <jglazer at gard.com>
Subject: Re: [Bldg-sim] IES-VE
To: bldg-sim at onebuilding.org
Message-ID: <4933E460.4030503 at gard.com>
Content-Type: text/plain; charset=ISO-8859-1; format=flowed

I would be glad to set up a new mailing list for users of 
IES-VE using onebuilding.org, all we need is a name. 
Unfortunately, I do not have permission to name the list 
IES-VE-users or VE-users or anything that might be 
trademarked. If someone can come up with a good name that is 
not trademarked, I will set up a new mailing list.

Jason

On 11/28/2008 6:03 PM, Joel Londenberg wrote:
> Some time ago there was mention of creating a forum/mailing list 
> specifically focused on the use of IES-VE.  Has this materialized, can 
> someone direct me to it?
> 
> 
> ------------------------------------------------------------------------
> 
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG

-- 
Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair
Admin for onebuilding.org building performance mailing lists


------------------------------

Message: 5
Date: Mon, 1 Dec 2008 09:09:01 -0500
From: "James V. Dirkes II  P.E." <jvd2pe at tds.net>
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and
    Glazing
To: "'Ulrik Welle-Strand Horn'" <ulrik.horn at silpainc.com>,
    <bldg-sim at lists.onebuilding.org>
Message-ID: <CDD0066E87F140BABCF7AC76453A10CE at BPT>
Content-Type: text/plain; charset="us-ascii"

Dear Ulrik,

Since the intent of the Standard is to assign the better glazing performance
to non-North walls, I always rotate the glazing characteristics with the
building. (e.g., I assign the "North" glazing characteristics to the
elevation that, after rotating, faces North)


The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653





  _____  

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ulrik
Welle-Strand Horn
Sent: Monday, December 01, 2008 7:30 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Appendix G - Base Case Orientations and Glazing


Dear all,

When you are rotating the building through 4 different orientations, do you
change the glazing so that the glazing with the highest SHGC is always faces
north, or do you put the glazing with high SHGC on the original north
facade, and then rotate the building so that the high SHGC glazing faces the
east, south and west orientations in subsequent simulations?

Yours faithfully,


Ulrik Welle-Strand Horn 
Sustainability Engineer


Silpa Inc.
s i m p l e  .  s c i e n t i f i c  .  s u s t a i n a b l e

AMERICAS | MIDDLE EAST | ASIA
www.silpainc.com <http://www.silpainc.com/> 


India: +91.90080.96083

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081201/5760c682/attachment-0001.htm>

------------------------------

Message: 6
Date: Mon, 1 Dec 2008 08:21:55 -0600
From: Paul Riemer <Paul.Riemer at dunhameng.com>
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and
    Glazing
To: "'James V. Dirkes II  P.E.'" <jvd2pe at tds.net>, 'Ulrik Welle-Strand
    Horn'    <ulrik.horn at silpainc.com>, "bldg-sim at lists.onebuilding.org"
    <bldg-sim at lists.onebuilding.org>
Message-ID:
    <057EF46662FE994F8119F0A903BCD0F8299BE6D91A at eml1.dunham.corp>
Content-Type: text/plain; charset="us-ascii"

I read Table G3.1 section 5 sub item (c) under the baseline building performance column to require use of the "SHGC_all" for all vertical glazing.  Have others read that and reached a different conclusion?  Did I miss an addenda? or a CIR?

From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James V. Dirkes II P.E.
Sent: Monday, December 01, 2008 8:09 AM
To: 'Ulrik Welle-Strand Horn'; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and Glazing

Dear Ulrik,

Since the intent of the Standard is to assign the better glazing performance to non-North walls, I always rotate the glazing characteristics with the building. (e.g., I assign the "North" glazing characteristics to the elevation that, after rotating, faces North)

The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653



________________________________
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ulrik Welle-Strand Horn
Sent: Monday, December 01, 2008 7:30 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Appendix G - Base Case Orientations and Glazing
Dear all,

When you are rotating the building through 4 different orientations, do you change the glazing so that the glazing with the highest SHGC is always faces north, or do you put the glazing with high SHGC on the original north facade, and then rotate the building so that the high SHGC glazing faces the east, south and west orientations in subsequent simulations?

Yours faithfully,


Ulrik Welle-Strand Horn
Sustainability Engineer

Silpa Inc.
s i m p l e  .  s c i e n t i f i c  .  s u s t a i n a b l e
AMERICAS | MIDDLE EAST | ASIA
www.silpainc.com<http://console.mxlogic.com/redir/?1psKUPuX9JdZZWXPPxI05ihWSOxrBYdTdTdA3Q29uABiV2Hsbvg57OFeDlxV1KhW4E4u00CTHFK6QkQTAmbI3APrypI5-Aq83iScDE4iZ9aCBQQg22OTMgA7Cy096y0Kq81Dquq81bquq80N6nMDIVlxgQgr10Qg18_hik29KvxYY1NJ4SyrjvvuKYYYrV6r6>

India: +91.90080.96083
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081201/0762c13b/attachment-0001.htm>

------------------------------

Message: 7
Date: Mon, 1 Dec 2008 09:37:16 -0500
From: "Brenda V. Morawa" <bren at bvm-engineering.com>
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and
    Glazing
To: "'Paul Riemer'" <Paul.Riemer at dunhameng.com>,    "'James V. Dirkes II
    P.E.'" <jvd2pe at tds.net>,    "'Ulrik Welle-Strand Horn'"
    <ulrik.horn at silpainc.com>,    <bldg-sim at lists.onebuilding.org>
Message-ID: <001d01c953c2$503ebee0$f0bc3ca0$@com>
Content-Type: text/plain; charset="us-ascii"

I agree and was looking for that reference as we speak!



Brenda V. Morawa, PE LEED AP QCxP

Co-Vice-Chair, USGBC LEED Certification Committee

BVMELogo3jpg

404.806.2018  EXT 101

404.210.6593 (cell)



From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Paul Riemer
Sent: Monday, December 01, 2008 9:22 AM
To: 'James V. Dirkes II P.E.'; 'Ulrik Welle-Strand Horn';
bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and Glazing



I read Table G3.1 section 5 sub item (c) under the baseline building
performance column to require use of the "SHGC_all" for all vertical
glazing.  Have others read that and reached a different conclusion?  Did I
miss an addenda? or a CIR?



From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James V. Dirkes
II P.E.
Sent: Monday, December 01, 2008 8:09 AM
To: 'Ulrik Welle-Strand Horn'; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and Glazing



Dear Ulrik,



Since the intent of the Standard is to assign the better glazing performance
to non-North walls, I always rotate the glazing characteristics with the
building. (e.g., I assign the "North" glazing characteristics to the
elevation that, after rotating, faces North)



The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653







  _____  

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ulrik
Welle-Strand Horn
Sent: Monday, December 01, 2008 7:30 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Appendix G - Base Case Orientations and Glazing

Dear all,

When you are rotating the building through 4 different orientations, do you
change the glazing so that the glazing with the highest SHGC is always faces
north, or do you put the glazing with high SHGC on the original north
facade, and then rotate the building so that the high SHGC glazing faces the
east, south and west orientations in subsequent simulations?

Yours faithfully,


Ulrik Welle-Strand Horn 
Sustainability Engineer


Silpa Inc.
s i m p l e  .  s c i e n t i f i c  .  s u s t a i n a b l e

AMERICAS | MIDDLE EAST | ASIA
www.silpainc.com
<http://console.mxlogic.com/redir/?1psKUPuX9JdZZWXPPxI05ihWSOxrBYdTdTdA3Q29u
ABiV2Hsbvg57OFeDlxV1KhW4E4u00CTHFK6QkQTAmbI3APrypI5-Aq83iScDE4iZ9aCBQQg22OTM
gA7Cy096y0Kq81Dquq81bquq80N6nMDIVlxgQgr10Qg18_hik29KvxYY1NJ4SyrjvvuKYYYrV6r6
> 


India: +91.90080.96083

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081201/2dc9fb09/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2325 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081201/2dc9fb09/attachment-0001.jpeg>

------------------------------

Message: 8
Date: Mon, 1 Dec 2008 20:12:08 +0530
From: "Ulrik Welle-Strand Horn" <ulrik.horn at silpainc.com>
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and
    Glazing
To: "Paul Riemer" <Paul.Riemer at dunhameng.com>
Cc: "bldg-sim at lists.onebuilding.org" <bldg-sim at lists.onebuilding.org>
Message-ID:
    <343a1a270812010642j72988fb5saf4873b9b2e5bf3 at mail.gmail.com>
Content-Type: text/plain; charset="iso-8859-1"

Paul,

That's a VERY valid point. Thanks for pointing it out.


*Ulrik Welle-Strand Horn *
Sustainability Engineer

*Silpa Inc.*
*s* i m p l e  .  *s* c i e n t i f i c  .  *s* u s t a i n a b l e
AMERICAS | MIDDLE EAST | ASIA
www.silpainc.com

India: +91.90080.96083

On Mon, Dec 1, 2008 at 7:51 PM, Paul Riemer <Paul.Riemer at dunhameng.com>wrote:

>  I read Table G3.1 section 5 sub item (c) under the baseline building
> performance column to require use of the "SHGC_all" for all vertical
> glazing.  Have others read that and reached a different conclusion?  Did I
> miss an addenda? or a CIR?
>
>
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *James V. Dirkes II
> P.E.
> *Sent:* Monday, December 01, 2008 8:09 AM
> *To:* 'Ulrik Welle-Strand Horn'; bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Appendix G - Base Case Orientations and Glazing
>
>
>
> Dear Ulrik,
>
>
>
> Since the intent of the Standard is to assign the better glazing
> performance to non-North walls, I always rotate the glazing characteristics
> with the building. (e.g., I assign the "North" glazing characteristics to
> the elevation that, after rotating, faces North)
>
>
>
> *The Building Performance Team
> James V. Dirkes II, P.E., LEED AP
> *1631 Acacia Drive NW
> Grand Rapids, MI 49504
> 616 450 8653
>
>
>
>
>
>
>  ------------------------------
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Ulrik Welle-Strand
> Horn
> *Sent:* Monday, December 01, 2008 7:30 AM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] Appendix G - Base Case Orientations and Glazing
>
> Dear all,
>
> When you are rotating the building through 4 different orientations, do you
> change the glazing so that the glazing with the highest SHGC is always faces
> north, or do you put the glazing with high SHGC on the original north
> facade, and then rotate the building so that the high SHGC glazing faces the
> east, south and west orientations in subsequent simulations?
>
> Yours faithfully,
>
>
> *Ulrik Welle-Strand Horn *
> Sustainability Engineer
>
>
> *Silpa Inc.*
> *s* i m p l e  .  *s* c i e n t i f i c  .  *s* u s t a i n a b l e
>
> AMERICAS | MIDDLE EAST | ASIA
> www.silpainc.com<http://console.mxlogic.com/redir/?1psKUPuX9JdZZWXPPxI05ihWSOxrBYdTdTdA3Q29uABiV2Hsbvg57OFeDlxV1KhW4E4u00CTHFK6QkQTAmbI3APrypI5-Aq83iScDE4iZ9aCBQQg22OTMgA7Cy096y0Kq81Dquq81bquq80N6nMDIVlxgQgr10Qg18_hik29KvxYY1NJ4SyrjvvuKYYYrV6r6>
>
>
> India: +91.90080.96083
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081201/c9a5e382/attachment-0001.htm>

------------------------------

Message: 9
Date: Mon, 01 Dec 2008 09:00:54 -0600
From: "Bill Talbert" <btalbert at aeieng.com>
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and
    Glazing
To: "Paul Riemer" <Paul.Riemer at dunhameng.com>,    "Ulrik Welle-Strand
    Horn" <ulrik.horn at silpainc.com>
Cc: "bldg-sim at lists.onebuilding.org" <bldg-sim at lists.onebuilding.org>
Message-ID: <4933A7C9.08AC.0005.0 at aeieng.com>
Content-Type: text/plain; charset="utf-8"

A90.1-2007 removed the reference to SHGC_All and refers to the Chapter 5
tables. You should be able to use the SHGC_north in the baseline if you
follow 2007.
Regards,


Bill Talbert, PE, LEED? AP
Mechanical Systems
Phone: (608) 441-6677
E-mail: btalbert at aeieng.com 

Affiliated Engineers Inc.
5802 Research Park Blvd.
Madison, WI. 53719
Tel. (608) 238-2616
Fax. (608) 238-2614


>>> "Ulrik Welle-Strand Horn" <ulrik.horn at silpainc.com> 12/1/2008 8:42
AM >>>
Paul, 

That's a VERY valid point. Thanks for pointing it out.


Ulrik Welle-Strand Horn 
Sustainability Engineer

Silpa Inc.
s i m p l e  .  s c i e n t i f i c  .  s u s t a i n a b l e
AMERICAS | MIDDLE EAST | ASIA
www.silpainc.com ( http://www.silpainc.com/ )

India: +91.90080.96083

On Mon, Dec 1, 2008 at 7:51 PM, Paul Riemer <Paul.Riemer at dunhameng.com>
wrote:



I read Table G3.1 section 5 sub item (c) under the baseline building
performance column to require use of the "SHGC_all" for all vertical
glazing.  Have others read that and reached a different conclusion?  Did
I miss an addenda? or a CIR?


From:bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James V.
Dirkes II P.E.
Sent: Monday, December 01, 2008 8:09 AM
To: 'Ulrik Welle-Strand Horn'; bldg-sim at lists.onebuilding.org 
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and
Glazing


Dear Ulrik,

Since the intent of the Standard is to assign the better glazing
performance to non-North walls, I always rotate the glazing
characteristics with the building. (e.g., I assign the "North" glazing
characteristics to the elevation that, after rotating, faces North)



The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653






From:bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ulrik
Welle-Strand Horn
Sent: Monday, December 01, 2008 7:30 AM
To: bldg-sim at lists.onebuilding.org 
Subject: [Bldg-sim] Appendix G - Base Case Orientations and Glazing
Dear all,

When you are rotating the building through 4 different orientations, do
you change the glazing so that the glazing with the highest SHGC is
always faces north, or do you put the glazing with high SHGC on the
original north facade, and then rotate the building so that the high
SHGC glazing faces the east, south and west orientations in subsequent
simulations?

Yours faithfully,


Ulrik Welle-Strand Horn 
Sustainability Engineer


Silpa Inc.
si m p l e  .  s c i e n t i f i c  .  s u s t a i n a b l e

AMERICAS | MIDDLE EAST | ASIA
www.silpainc.com (
http://console.mxlogic.com/redir/?1psKUPuX9JdZZWXPPxI05ihWSOxrBYdTdTdA3Q29uABiV2Hsbvg57OFeDlxV1KhW4E4u00CTHFK6QkQTAmbI3APrypI5-Aq83iScDE4iZ9aCBQQg22OTMgA7Cy096y0Kq81Dquq81bquq80N6nMDIVlxgQgr10Qg18_hik29KvxYY1NJ4SyrjvvuKYYYrV6r6
)


India: +91.90080.96083


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081201/4583c910/attachment-0001.htm>

------------------------------

Message: 10
Date: Mon, 1 Dec 2008 10:01:26 -0500
From: "James Hansen" <JHANSEN at ghtltd.com>
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and
    Glazing
To: <bldg-sim at lists.onebuilding.org>
Message-ID:
    <25F2BDB6656B8F40A1289ED906D6B5CF038E12DA at EXCHANGE1.cadd_group.ghtltd.com>
    
Content-Type: text/plain; charset="us-ascii"

This is an interesting discussion (one that may have already occurred
previously).  According to the 90.1 User Manual:



"SHGC - The budget building design's fenestration solar heat gain
coefficient is set to the maximum required for the climate.  The
prescriptive standards give SHGC criteria for all orientations and
provide an exception for north facing fenestration.  The exception is
not used for the baseline building; the criteria for all orientations
are used for all orientations..."



However, even the LEED-NC EAc1 template differentiates between the North
SHGC and the rest of the fenestration....if the exception is not to be
used, why would the USGBC have a place to enter the SHGC(north) for the
baseline building??  And why would they accept two different SHGCs for
the baseline building on the template?



I can't seem to find any NC or CS CIRs that address this.



GHT Limited
James Hansen, PE, LEED AP

Senior Associate

1010 N. Glebe Rd, Suite 200

Arlington, VA  22201-4749

703-338-5754 (Cell)

703-243-1200 (Office)

703-276-1376 (Fax)

www.ghtltd.com <http://www.ghtltd.com/> 



From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ulrik
Welle-Strand Horn
Sent: Monday, December 01, 2008 9:42 AM
To: Paul Riemer
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and Glazing



Paul, 

That's a VERY valid point. Thanks for pointing it out.


Ulrik Welle-Strand Horn 
Sustainability Engineer


Silpa Inc.
s i m p l e  .  s c i e n t i f i c  .  s u s t a i n a b l e

AMERICAS | MIDDLE EAST | ASIA
www.silpainc.com <http://www.silpainc.com/> 


India: +91.90080.96083

On Mon, Dec 1, 2008 at 7:51 PM, Paul Riemer <Paul.Riemer at dunhameng.com>
wrote:

I read Table G3.1 section 5 sub item (c) under the baseline building
performance column to require use of the "SHGC_all" for all vertical
glazing.  Have others read that and reached a different conclusion?  Did
I miss an addenda? or a CIR?



From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James V.
Dirkes II P.E.
Sent: Monday, December 01, 2008 8:09 AM
To: 'Ulrik Welle-Strand Horn'; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and Glazing



Dear Ulrik,



Since the intent of the Standard is to assign the better glazing
performance to non-North walls, I always rotate the glazing
characteristics with the building. (e.g., I assign the "North" glazing
characteristics to the elevation that, after rotating, faces North)



The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653







________________________________

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ulrik
Welle-Strand Horn
Sent: Monday, December 01, 2008 7:30 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Appendix G - Base Case Orientations and Glazing

Dear all,

When you are rotating the building through 4 different orientations, do
you change the glazing so that the glazing with the highest SHGC is
always faces north, or do you put the glazing with high SHGC on the
original north facade, and then rotate the building so that the high
SHGC glazing faces the east, south and west orientations in subsequent
simulations?

Yours faithfully,


Ulrik Welle-Strand Horn 
Sustainability Engineer


Silpa Inc.
s i m p l e  .  s c i e n t i f i c  .  s u s t a i n a b l e

AMERICAS | MIDDLE EAST | ASIA
www.silpainc.com
<http://console.mxlogic.com/redir/?1psKUPuX9JdZZWXPPxI05ihWSOxrBYdTdTdA3
Q29uABiV2Hsbvg57OFeDlxV1KhW4E4u00CTHFK6QkQTAmbI3APrypI5-Aq83iScDE4iZ9aCB
QQg22OTMgA7Cy096y0Kq81Dquq81bquq80N6nMDIVlxgQgr10Qg18_hik29KvxYY1NJ4Syrj
vvuKYYYrV6r6> 


India: +91.90080.96083




The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee.  It is the property of GHT Limited.  Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful.  If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to ght at ghtltd.com, and destroy this communication and all copies thereof, including all attachments.  Thank you.



-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081201/73d57808/attachment-0001.htm>

------------------------------

Message: 11
Date: Mon, 1 Dec 2008 10:10:15 -0500
From: "James Hansen" <JHANSEN at ghtltd.com>
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and
    Glazing
To: <bldg-sim at lists.onebuilding.org>
Message-ID:
    <25F2BDB6656B8F40A1289ED906D6B5CF038E12DB at EXCHANGE1.cadd_group.ghtltd.com>
    
Content-Type: text/plain; charset="us-ascii"

Sorry, I should have read further before posting.  In the LEED-NC
reference guide, it states:



"The four Baseline Design energy models are identical to each other,
except that the building orientation for each model is modified as
described in ASHRAE Std 90.1 Table G3.5.1a, and the window SHGCs are
revised to reflect the minimum ASHRAE Building Envelope Requirements for
the revised building orientation."



In other words, the USGBC, whether on purpose or not, has provided its
own exception to 90.1 that allows you to use the SHGC(north) in the
baseline models.  And yes, after rotating, you have to reassign the
proper SHGCs to the new "north".



GHT Limited
James Hansen, PE, LEED AP

Senior Associate

1010 N. Glebe Rd, Suite 200

Arlington, VA  22201-4749

703-338-5754 (Cell)

703-243-1200 (Office)

703-276-1376 (Fax)

www.ghtltd.com <http://www.ghtltd.com/> 



From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James
Hansen
Sent: Monday, December 01, 2008 10:01 AM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and Glazing



This is an interesting discussion (one that may have already occurred
previously).  According to the 90.1 User Manual:



"SHGC - The budget building design's fenestration solar heat gain
coefficient is set to the maximum required for the climate.  The
prescriptive standards give SHGC criteria for all orientations and
provide an exception for north facing fenestration.  The exception is
not used for the baseline building; the criteria for all orientations
are used for all orientations..."



However, even the LEED-NC EAc1 template differentiates between the North
SHGC and the rest of the fenestration....if the exception is not to be
used, why would the USGBC have a place to enter the SHGC(north) for the
baseline building??  And why would they accept two different SHGCs for
the baseline building on the template?



I can't seem to find any NC or CS CIRs that address this.



GHT Limited
James Hansen, PE, LEED AP

Senior Associate

1010 N. Glebe Rd, Suite 200

Arlington, VA  22201-4749

703-338-5754 (Cell)

703-243-1200 (Office)

703-276-1376 (Fax)

www.ghtltd.com <http://www.ghtltd.com/> 



From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ulrik
Welle-Strand Horn
Sent: Monday, December 01, 2008 9:42 AM
To: Paul Riemer
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and Glazing



Paul, 

That's a VERY valid point. Thanks for pointing it out.


Ulrik Welle-Strand Horn 
Sustainability Engineer


Silpa Inc.
s i m p l e  .  s c i e n t i f i c  .  s u s t a i n a b l e

AMERICAS | MIDDLE EAST | ASIA
www.silpainc.com <http://www.silpainc.com/> 


India: +91.90080.96083

On Mon, Dec 1, 2008 at 7:51 PM, Paul Riemer <Paul.Riemer at dunhameng.com>
wrote:

I read Table G3.1 section 5 sub item (c) under the baseline building
performance column to require use of the "SHGC_all" for all vertical
glazing.  Have others read that and reached a different conclusion?  Did
I miss an addenda? or a CIR?



From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James V.
Dirkes II P.E.
Sent: Monday, December 01, 2008 8:09 AM
To: 'Ulrik Welle-Strand Horn'; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and Glazing



Dear Ulrik,



Since the intent of the Standard is to assign the better glazing
performance to non-North walls, I always rotate the glazing
characteristics with the building. (e.g., I assign the "North" glazing
characteristics to the elevation that, after rotating, faces North)



The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653







________________________________

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ulrik
Welle-Strand Horn
Sent: Monday, December 01, 2008 7:30 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Appendix G - Base Case Orientations and Glazing

Dear all,

When you are rotating the building through 4 different orientations, do
you change the glazing so that the glazing with the highest SHGC is
always faces north, or do you put the glazing with high SHGC on the
original north facade, and then rotate the building so that the high
SHGC glazing faces the east, south and west orientations in subsequent
simulations?

Yours faithfully,


Ulrik Welle-Strand Horn 
Sustainability Engineer


Silpa Inc.
s i m p l e  .  s c i e n t i f i c  .  s u s t a i n a b l e

AMERICAS | MIDDLE EAST | ASIA
www.silpainc.com
<http://console.mxlogic.com/redir/?1psKUPuX9JdZZWXPPxI05ihWSOxrBYdTdTdA3
Q29uABiV2Hsbvg57OFeDlxV1KhW4E4u00CTHFK6QkQTAmbI3APrypI5-Aq83iScDE4iZ9aCB
QQg22OTMgA7Cy096y0Kq81Dquq81bquq80N6nMDIVlxgQgr10Qg18_hik29KvxYY1NJ4Syrj
vvuKYYYrV6r6> 


India: +91.90080.96083



________________________________

The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee.  It is
the property of GHT Limited.  Unauthorized use, disclosure or copying of
this communication or any part thereof is strictly prohibited and may be
unlawful.  If you have received this communication in error, please
notify me immediately by return e-mail or by e-mail to ght at ghtltd.com
<mailto:ght at ghtltd.com> , and destroy this communication and all copies
thereof, including all attachments.  Thank you.


The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee.  It is the property of GHT Limited.  Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful.  If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to ght at ghtltd.com, and destroy this communication and all copies thereof, including all attachments.  Thank you.



-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081201/2853a28b/attachment-0001.htm>

------------------------------

Message: 12
Date: Mon, 1 Dec 2008 09:12:21 -0800 (PST)
From: "Nathan Miller" <nathanm at rushingco.com>
Subject: Re: [Bldg-sim] calculating the mean monthly outdoor temp
To: "'Chris Yates'" <Chris at zed-uk.com>,    "'Building Simulation'"
    <bldg-sim at lists.onebuilding.org>
Message-ID: <008301c953d7$f42c7c80$dc857580$@com>
Content-Type: text/plain;    charset="US-ASCII"

I'm no statistician, but I've always been dubious about that calculation.
You are taking the mean of two means, which seems to be getting farther
and farther from actual data.

It also seems to punish some of the climates that are best suited for
natural ventilation, since having cool nights significantly drops the
acceptability limits. I assume they are pushing you to take advantage of
night pre-cooling and thermal mass, but I find it curious that there are
no allowable hours outside of the range. All of the pre-cooling in the
world isn't going to help you keep the temperatures down during that one
string of 90 degree days in the tmy2 file...

Nathan Miller

Senior Energy Engineer/Mechanical Engineer

direct: 206.788.4577

fax: 206.285.7111 

-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Chris Yates
Sent: Friday, November 28, 2008 2:30 AM
To: Building Simulation
Subject: Re: [Bldg-sim] calculating the mean monthly outdoor temp

There is a small difference between the arithmetic mean of the monthly 
mean max and min and the overall arithmetic mean of 720 hours of weather 
data. Like you say, it's probably a legacy from the old pen and paper
days.
I've heard that some would use occupied period only to calculate the 
mean. However, I can not find any reference in the text of A55 to 
justify this. Being able to average the warmer occupied hours would make 
things a whole lot easier - even the 80% acceptability temperature can 
regularly be lower than the summertime peaks. It's a tough call for 
natural ventilation.

Many thanks

Chris

Joe Huang wrote:
> The cited method sounds like a carry-over from when stations reported 
> only max/min temperatures.
> If hourly data is available, why wouldn't you just calculate the mean 
> of all the temperatures ?
>
> Joe Huang
> White Box Technologies
>
> ----- Original Message ----- From: "Chris Yates" <Chris at zed-uk.com>
> To: "Building Simulation" <bldg-sim at lists.onebuilding.org>
> Sent: Thursday, November 27, 2008 1:58 PM
> Subject: [Bldg-sim] calculating the mean monthly outdoor temp
>
>
>> For the purpose of acceptability limits, can anybody cite any 
>> guidance on calculating the mean monthly outdoor temperature? I've 
>> read ASHRAE 55 and it states: "mean monthly outdoor temperature is 
>> the arithmetic average of the mean daily minimum and the mean daily 
>> maximum outdoor (dry bulb) temperature for the month in question."
>> Thanks
>> _______________________________________________
>> Bldg-sim mailing list
>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>> To unsubscribe from this mailing list send  a blank message to 
>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>
>
>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG


------------------------------

Message: 13
Date: Mon, 01 Dec 2008 10:22:07 -0700
From: "Fred Porter" <FPorter at archenergy.com>
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and
    Glazing
To: "Bill Talbert" <btalbert at aeieng.com>,    "Paul Riemer"
    <Paul.Riemer at dunhameng.com>,    "Ulrik Welle-Strand Horn"
    <ulrik.horn at silpainc.com>
Cc: "bldg-sim at lists.onebuilding.org" <bldg-sim at lists.onebuilding.org>,
    901ecb at gard.com
Message-ID: <4933BACE.0661.0093.0 at archenergy.com>
Content-Type: text/plain; charset="us-ascii"

All;
I certainly do NOT think the 2007 PRM requires that the baseline glazing "North" SHGCs be "moved" as the "North" exposures change in each of the simulations that generates the "baseline building performance." I could see how one might think that, but say it ain't so. I assume the baseline "North" SHGC is applied to what would be "North" glazing in the proposed and unrotated baseline models, and those glazing parameters are left in place for that facade as the baseline model is rotated. I don't think this has been fodder for a USGBC CIR or ASHRAE interpretation yet, but maybe I'm out of touch. Addendum A to 2004, which removed the glazing redistribution requirement, still used SHGC_all for all baseline glazing. I thought this had been incorporated verbatim in the 2007 edits but noooooo. Time to get out the magnifier and channel my inner attorney.

Fred

>>> "Bill Talbert" <btalbert at aeieng.com> 12/1/2008 8:00 AM >>>
A90.1-2007 removed the reference to SHGC_All and refers to the Chapter 5 tables. You should be able to use the SHGC_north in the baseline if you follow 2007.
Regards,





From:bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James V. Dirkes II P.E.
Sent: Monday, December 01, 2008 8:09 AM
To: 'Ulrik Welle-Strand Horn'; bldg-sim at lists.onebuilding.org 
Subject: Re: [Bldg-sim] Appendix G - Base Case Orientations and Glazing

Dear Ulrik,
Since the intent of the Standard is to assign the better glazing performance to non-North walls, I always rotate the glazing characteristics with the building. (e.g., I assign the "North" glazing characteristics to the elevation that, after rotating, faces North)

From:bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ulrik Welle-Strand Horn
Sent: Monday, December 01, 2008 7:30 AM
To: bldg-sim at lists.onebuilding.org 
Subject: [Bldg-sim] Appendix G - Base Case Orientations and Glazing
Dear all,

When you are rotating the building through 4 different orientations, do you change the glazing so that the glazing with the highest SHGC is always faces north, or do you put the glazing with high SHGC on the original north facade, and then rotate the building so that the high SHGC glazing faces the east, south and west orientations in subsequent simulations?

Yours faithfully,


Ulrik Welle-Strand Horn 
Sustainability Engineer


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081201/0d6298ce/attachment-0001.htm>

------------------------------

Message: 14
Date: Mon, 01 Dec 2008 13:02:52 -0500
From: JRR <energy.wwind at cox.net>
Subject: Re: [Bldg-sim] calculating the mean monthly outdoor temp
To: Nathan Miller <nathanm at rushingco.com>,
    bldg-sim at lists.onebuilding.org
Message-ID: <493426CC.9050708 at cox.net>
Content-Type: text/plain; charset="iso-8859-1"; Format="flowed"

John Ross wrote;

Using a mean monthly temperature ties the hands of innovative engineers 
in opportune climates.
In Northern Virginia I use an opening roof skylight to dump excessive 
solar gain in the late afternoon.
This operational variation is only practiced the last week of September 
to the second week of October
depending depending on  the particular year's weather

It would be appropriate to use mean monthly temperature for calculating 
long term Geothermal field
effects on the  other hand.......


Nathan Miller wrote:
> I'm no statistician, but I've always been dubious about that calculation.
> You are taking the mean of two means, which seems to be getting farther
> and farther from actual data.
>
> It also seems to punish some of the climates that are best suited for
> natural ventilation, since having cool nights significantly drops the
> acceptability limits. I assume they are pushing you to take advantage of
> night pre-cooling and thermal mass, but I find it curious that there are
> no allowable hours outside of the range. All of the pre-cooling in the
> world isn't going to help you keep the temperatures down during that one
> string of 90 degree days in the tmy2 file...
>
> Nathan Miller
>
> Senior Energy Engineer/Mechanical Engineer
>
> direct: 206.788.4577
>
> fax: 206.285.7111 
>
> -----Original Message-----
> From: bldg-sim-bounces at lists.onebuilding.org
> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Chris Yates
> Sent: Friday, November 28, 2008 2:30 AM
> To: Building Simulation
> Subject: Re: [Bldg-sim] calculating the mean monthly outdoor temp
>
> There is a small difference between the arithmetic mean of the monthly 
> mean max and min and the overall arithmetic mean of 720 hours of weather 
> data. Like you say, it's probably a legacy from the old pen and paper
> days.
> I've heard that some would use occupied period only to calculate the 
> mean. However, I can not find any reference in the text of A55 to 
> justify this. Being able to average the warmer occupied hours would make 
> things a whole lot easier - even the 80% acceptability temperature can 
> regularly be lower than the summertime peaks. It's a tough call for 
> natural ventilation.
>
> Many thanks
>
> Chris
>
> Joe Huang wrote:
>  
>> The cited method sounds like a carry-over from when stations reported 
>> only max/min temperatures.
>> If hourly data is available, why wouldn't you just calculate the mean 
>> of all the temperatures ?
>>
>> Joe Huang
>> White Box Technologies
>>
>> ----- Original Message ----- From: "Chris Yates" <Chris at zed-uk.com>
>> To: "Building Simulation" <bldg-sim at lists.onebuilding.org>
>> Sent: Thursday, November 27, 2008 1:58 PM
>> Subject: [Bldg-sim] calculating the mean monthly outdoor temp
>>
>>
>>    
>>> For the purpose of acceptability limits, can anybody cite any 
>>> guidance on calculating the mean monthly outdoor temperature? I've 
>>> read ASHRAE 55 and it states: "mean monthly outdoor temperature is 
>>> the arithmetic average of the mean daily minimum and the mean daily 
>>> maximum outdoor (dry bulb) temperature for the month in question."
>>> Thanks
>>> _______________________________________________
>>> Bldg-sim mailing list
>>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>>> To unsubscribe from this mailing list send  a blank message to 
>>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>>
>>>      
>>
>>    
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>  
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081201/044e35d8/attachment-0001.htm>

------------------------------

Message: 15
Date: Mon, 1 Dec 2008 12:55:08 -0700
From: "Josh K" <jeemang at gmail.com>
Subject: Re: [Bldg-sim] DOE-2.2 geometry import troubles
To: "Brandon Nichols" <bwnichols at gmail.com>
Cc: bldg-sim at lists.onebuilding.org
Message-ID:
    <531759080812011155r4275050bn599212d646904d2d at mail.gmail.com>
Content-Type: text/plain; charset="iso-8859-1"

Hi Brandon;

I've been doing some "reverse engineering," and I keep coming back to the
same problem: my FLOOR AND SPACE polygons appear in eQuest exactly where I
expect them to, but all of the EXTERIOR-WALL polygons, if no translations
are applied (ie X, Y, Z, AZIMUTH, TILT = 0) , appear rotated 180 degrees
around the building coordinate X axis relative to where I would expect them
to be. Also, oddly, the TILT and AZIMUTH transformations, when specified,
take place relative to this rotated coordinate system -- ie, the AZIMUTH
rotation is about the buidling coordinate *negative *z-axis -- while the
translation transformation (as specified by X, Y, and Z) take place as
expected (in the building coordinate system).

Very strange stuff. I get the feeling that this has something to do with the
EXTERIOR-WALL coordinate system being dependant on the SPACE coordinate
system which is, in turn, dependant on the FLOOR coordinate system. As it
stands, my FLOOR, SPACE, and EXTERIOR WALL object that represents the floor
all use the same POLYGON object -- does anyone know if this in itself is a
problem? My instinct is that I'm somehow misunderstanding this relationship,
but I've done some fiddling in this regard and haven't been able to change
very much...

Again, if anyone has any insight on this issue, it would be greatly
appreciated.

Thanks a lot,

Josh

On Fri, Nov 7, 2008 at 1:47 AM, Brandon Nichols <bwnichols at gmail.com> wrote:

> Suggest reverse engineering...define your objective in eQuest (starting
> with the lower-leftmost vertex for all polygons) and compare the resulting
> inp file to yours.  Also take a close look at the DOE2.2 documentation,
> wherein the coordinate system is detailed.
>
> Suspected root cause issue is the disconnect going from the eQuest
> Floor/Zone editor, where all zone (space) coordinates are entered absolute,
> to the .inp file where the eQuest stores coordinates of space polygons
> relative to the floor polygon.
>
> Suggest always starting all polygons with the lower-leftmost vertex, to
> help make sense of the relative coordinates and azimuths.  This habit is one
> you'll be glad to have acquired, should dissecting inp files become your
> muse.
>
> Regards
>
> Brandon Nichols
> BW Nichols PE
> Seattle WA
>
>
> On Nov 6, 2008 4:34 PM, "Josh K" <jeemang at gmail.com> wrote:
>
> Hi all;
>
> I'm trying to figure out how to manually enter geometry in DOE-2.2 and I'm
> having a little bit of trouble. My problems are myriad, but they essentially
> boil down to this: when I enter
>
> polygon.0 = POLYGON
>   V1 = (0.0,0.0)
>   V2 = (200,0)
>   V3 = (200,300)
>   V4 = (0,300)
>   ..
>
> floor.0 = FLOOR
>   AZIMUTH = 360
>   POLYGON = polygon.0
>   SHAPE = POLYGON
>   FLOOR-HEIGHT = 3.28
>   SPACE-HEIGHT = 3.28
>   ..
>
> space.0 = SPACE
>   ZONE-TYPE = UNCONDITIONED
>   POLYGON = polygon.0
>   SHAPE = POLYGON
>   ..
>
> face.0 = EXTERIOR-WALL
>   POLYGON = polygon.0
>   X = 0
>   Y = 0
>   Z = 0.0
>   AZIMUTH = 0.0
>   TILT = 0.0
>   CONSTRUCTION = "EWall Construction"
>   ..
>
> and import it to eQuest (the only good way I can think of to check if I've
> entered my geometry correctly), the resulting EXTERIOR-WALL surface is not
> where I expect it to be. I was expecting it to be in "NE" quadrant of the
> the building's XY plane, but instead it's in the "SW" quadrant, as if it had
> been rotated 180 degrees about the building coordinate system's z-axis.
> Puzzlingly, the SPACE and FLOOR objects appear where I would expect them to
> -- in the building's "NE" quadrant.
>
> Clearly I'm misunderstanding something about how POLYGON objects are to be
> positioned. If anyone could help me to understand what I've got wrong, I
> would greatly appreciate it.
>
> Many thanks,
>
> Josh
>
>
> --
> Josh Kjenner, EIT, LEED AP
> Manasc Isaac Architects Ltd.
> 10225 100 Avenue :: Edmonton, AB T5J 0A1
> 780.429.3977
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>


-- 
Josh Kjenner, EIT, LEED AP
Manasc Isaac Architects Ltd.
10225 100 Avenue :: Edmonton, AB T5J 0A1
780.429.3977
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081201/9a1aff84/attachment-0001.htm>

------------------------------

_______________________________________________
Bldg-sim mailing list
Bldg-sim at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org


End of Bldg-sim Digest, Vol 13, Issue 1
***************************************



      __________________________________________________________________
Looking for the perfect gift? Give the gift of Flickr! 

http://www.flickr.com/gift/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081201/aa617fbe/attachment.htm>