[Bldg-sim] Window

Carlos Alonso carlos.alonso at iesve.com
Tue Feb 19 09:33:30 PST 2008


Cramer,
LEED-NC 2.2 does NOT accept addenda of the Appendix G. Not only the fenestration distribution but any of the requirements changed in any of the addenda are NOT accepted. It is in the definition of the Credit EA1 Optimize Energy Performance. There is also a CIR posted in the usgbc website on the 4/25/2007 for this credit where this question is explained.

Hope it helps,
Carlos




Carlos Alonso 
Software Analyst 

T: +44 (0) 141 945 8500 
F: +44 (0) 141 945 8501 
http://www.iesve.com 

**Design, Simulate + Innovate with the <Virtual Environment>**

Integrated Environmental Solutions Limited. Registered in Scotland No. SC151456 
Registered Office - Helix Building, West Of Scotland Science Park, Glasgow G20 0SP

Email Disclaimer













-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Cramer Silkworth
Sent: 19 February 2008 11:23
To: umit.esiyok at uni-dortmund.de
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Window

Umit,

Addendum A removes that statement about uniform distribution, but does not change the area limits. As of April 2007 a design team may use addenda, but you must apply it to the entire LEED submittal (not necessarily all of the addenda, you can use just one if you like, as far as I know)- so you need to read all of Addendum A and follow all of its changes if you want to avoid the area distribution nonsense.

You can find the addenda here: http://www.ashrae.org/technology/page/132 

If there are other modifications to the 40% area limit I don't know of them.

J. Cramer Silkworth
silkworth at transsolar.com 
+49 0711-67976-182
Transsolar Energietechnik GmbH
http://www.transsolar.com
Stuttgart - Munich - New York 

Climate Engineering: Technologies for energy-efficiency and user comfort in buildings.
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart, Germany

Amtsgericht Stuttgart -  HRB 23347 / USt-IdNr.: 99073/00911

Partners: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer, Dipl.Phys. Stefan Holst 



-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ümit Esiyok
Sent: Tuesday, February 19, 2008 12:09 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Window

Dear all,

I simulate an office building from ASHRAE Table G3.1 I read that "Vertical fenestration areas for new buildings and additions shall equal that in the Proposed design or 40 % groß above grade wall, whichever is smaller, an shall be distrubuted uniformly..."
My office building has in reality almost 80 % fenestration area.
my first Qeustion is;
1)in Proposed and Baseline design the fenestration area must be same or not?
2)in both cases should window area be less than 40%?
3)I read from this email group that 40 % fenestration area requirement not aplicable anymore ? is that right?


--
Ümit Esiyok


_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG


_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG





More information about the Bldg-sim mailing list