Christopher:
Simply make them separate shells (in the Design development or DD
Wizard), just as if you were making serrate building floors (shells).
Screen 2 then allows you in EACH case to set up a flat or sloped roof.
If you need a specific roof angle, you should STILL create the two
shells (areas), then create the sloped roof in the Detailed Interface
with a roof tilt.
John R. Aulbach, PE, CEM
Project Manager
Nexant, Inc.
701 West Kimberly Ave., Suite 245
Placentia, CA 92870-6342 USA
Phone: 714-524-4402
Fax: 714-524-4407
email: jaulbach at nexant.com
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Christopher
Sturdivant
Sent: Thursday, February 21, 2008 1:26 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] e-quest software question
I have a question of using E-Quest of some areas that I'm unsure of:
I am running an energy model of a building that has a flat roof on one
side and on the other side has a sloped roof with a drywall ceiling.
How do I take in account of this without having to perform separate
energy models on the same building?
Thanks
Christopher Sturdivant
Design Engineer-Mechanical
RMF Engineering, Inc.
Ph: 843-971-9639 ext. 110
Fax: 843-971-9641
csturdiv at rmf.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080221/d06afa9c/attachment-0002.htm>
More information about the Bldg-sim
mailing list