[Bldg-sim] Supply temperature reset in ASHRAE baseline

Andrew Craig andrew_c at ieice.com
Thu Feb 28 17:14:26 PST 2008


Ying---

In the Public Review Draft of Appendix G that will appear in ASHRAE
90.1-2007, they revised G.1.3.12 to read: "The air temperature for
cooling shall be reset higher by 5 deg F..."  So I think you are fine in
just creating a cooling reset schedule.

Regards,

Andrew Craig, EIT,LEED AP/ Mechanical Designer 
INTERFACE ENGINEERING 
direct 503.382.2696 

-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of
yizhao1 at vt.edu
Sent: Thursday, February 28, 2008 5:00 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Supply temperature reset in ASHRAE baseline

Hi -
In the baseline, ASHRAE requires a supply air temperature reset for
system 5,
packaged rooftop VAV w/ reheat (G3.1.3.12). In the air side system
level, I can
set up a schedule for cool control, but heat control is in grey.
Does anyone know how to input the reset in the system? Economizer is
inlcuded.

Thanks!

Ying

_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG




More information about the Bldg-sim mailing list