[Bldg-sim] FW: [BLDG-SIM] 90.1-2004 Appendix G Glazing for Baselinecase

Andrew Craig andrew_c at ieice.com
Fri Jan 25 12:56:57 PST 2008


Mark---


The change occurred in addendum a to 90.1-2004.  Here is the text:

 

 

 

 

Andrew Craig, EIT,LEED AP/ Mechanical Designer 

INTERFACE ENGINEERING 

direct 503.382.2696 

 

-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Zoeteman,
Mark R.
Sent: Friday, January 25, 2008 12:44 PM
To: Bldg-Sim
Subject: [Bldg-sim] FW: [BLDG-SIM] 90.1-2004 Appendix G Glazing for
Baselinecase

 

I've reviewed all the 90.1-2004 addenda and don't see where vertical

fenestration requirement of "distributing uniformly in horizontal bands

across the four orientations" has been removed. Addenda "as" which

refers to this section doesn't remove either.

 

Mark Zoeteman, FTC&H 

-----Original Message-----

From: Zoeteman, Mark R. 

Sent: Friday, January 25, 2008 3:40 PM

To: 'Michael.Rosenberg at state.or.us'; BLDG-SIM at gard.com

Subject: RE: [BLDG-SIM] 90.1-2004 Appendix G Glazing for Baseline case

 

 

-----Original Message-----

From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Michael

Rosenberg

Sent: Wednesday, May 16, 2007 1:47 PM

To: BLDG-SIM at gard.com

Subject: [BLDG-SIM] 90.1-2004 Appendix G Glazing for Baseline case

 

The requirement to  distribute fenestration uniformly in horizontal

bands across the four orientations has been removed from Appendix G in

the published Addenda Supplement to 90.1, 2004. See the ASHRAE website

for the supplement.

 

http://www.ashrae.org/technology/page/132

 

 

 

 

Michael Rosenberg

Oregon Department of Energy

625 Marion St. N.E.

Salem, OR 97301-3742

Phone : (503) 373-7809

Fax: (503) 373-7806

 

>>> Chris Jones <cj at cr-jay.ca> 5/16/2007 9:56:02 AM >>>

Appendix G notes that for the Baseline building: "Vertical fenestration

areas for new buildings and additions shall equal that in the proposed

design or 40% of gross above grade wall area, whichever is smaller, and

shall be distributed uniformly in horizontal bands across the four

orientations."

Does this mean that the Baseline building gets windows on all walls on

each orientation whether or not the Design case has a window in all

walls on each orientation.  For example, if the west orientation has 30%

glazing overall but many spaces have no windows - some walls on the west

face have more that 30%.  Do those spaces in the Baseline case get 30%

glazing?  Or do I only put windows in the Baseline case where there are

windows in the Design case.

 

Thanks for any help!

 

 

 

 

 

 

 

Chris Jones, P.Eng.

14 Oneida Avenue

Toronto, ON M5J2E3

Tel. 416 203-7465

Fax. 416 946-1005 

 

======================================================

You received this e-mail because you are subscribed to the

BLDG-SIM at GARD.COM mailing list.  To unsubscribe from this mailing list

send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM

 

======================================================

You received this e-mail because you are subscribed to the

BLDG-SIM at GARD.COM mailing list.  To unsubscribe from this mailing list

send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM

 

_______________________________________________

Bldg-sim mailing list

Bldg-sim at lists.onebuilding.org

http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080125/b12381b2/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 40818 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080125/b12381b2/attachment-0001.jpeg>


More information about the Bldg-sim mailing list