[Bldg-sim] Shading projections-baseline building (LEED)
Kevin Kyte
kkyte at robsonwoese.com
Tue Mar 25 14:00:33 PDT 2008
Appendix G states the baseline model "does not shade itself", this simply
means that the envelope of the baseline model should have surface shading
turned off. You should have surface shading turned on for the proposed
model.
Kevin Kyte, LEED AP
RobsonWoese, Inc.
(T) 716-636-1800
(F) 716-636-1856
http://robsonwoese.com
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Myrene Giuliani
Sent: Tuesday, March 25, 2008 12:24 PM
To: Energy Modeling
Subject: [Bldg-sim] Shading projections-baseline building (LEED)
When constructing the baseline energy model, Appendix
G of ASHRAE 90.1 parameters specify that shading
projections are not to be included for the baseline
model. My question is, if the design of the building
includes balconies (it's a mid-rise residential
building) would they be considered shading
projections? My impression is that they are shading
projections, but I would like to confirm before
detailing the energy model.
Thank you,
Myrene Giuliani, LEED AP
____________________________________________________________________________
________
Be a better friend, newshound, and
know-it-all with Yahoo! Mobile. Try it now.
http://mobile.yahoo.com/;_ylt=Ahu06i62sR8HDtDypao8Wcj9tAcJ
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
More information about the Bldg-sim
mailing list