[Bldg-sim] Equest - Space Cooling Provided by Natural Gas!?
Doebber, Ian
Ian_Doebber at nrel.gov
Fri Mar 14 15:44:13 PDT 2008
John
You got it!! Thanks for looking into this. I remember entering it a
while ago to look into what preconditioning Equest could do. I really
appreciate it.
Ian
________________________________
From: Aulbach, John [mailto:jaulbach at nexant.com]
Sent: Friday, March 14, 2008 2:43 PM
To: Doebber, Ian; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Equest - Space Cooling Provided by Natural Gas!?
Possible answer.
Your Flr 1 East VAV has a Solid Desiccant System attached to it, the
only system which does. As I perceive it, Desiccant is a
dehumidification device, which eQuest MAY interpret as cooling. You
attach it to a hot water loop to recharge the desiccant, so gas is used
for a "cooling" purpose.
See how that flies in Sioux City.
John
________________________________
From: Doebber, Ian [mailto:Ian_Doebber at nrel.gov]
Sent: Friday, March 14, 2008 12:11 PM
To: Aulbach, John
Subject: RE: [Bldg-sim] Equest - Space Cooling Provided by Natural Gas!?
Sure thing.
Thanks
Ian
________________________________
From: Aulbach, John [mailto:jaulbach at nexant.com]
Sent: Friday, March 14, 2008 1:10 PM
To: Doebber, Ian
Subject: RE: [Bldg-sim] Equest - Space Cooling Provided by Natural Gas!?
Would you mind sending me your eQuest .PD2 and .INP file? It's hard to
guess over the airwaves.
John R. Aulbach, PE, CEM
Project Manager
Nexant, Inc.
701 West Kimberly Ave., Suite 245
Placentia, CA 92870-6342 USA
Phone: 714-524-4402
Fax: 714-524-4407
email: jaulbach at nexant.com
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Doebber,
Ian
Sent: Friday, March 14, 2008 12:02 PM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Equest - Space Cooling Provided by Natural Gas!?
I specified only an electric screw chiller. There is no "Engine Driven"
chiller or any piece of equipment that provides cooling which consumes
Natural Gas.
________________________________
From: Aulbach, John [mailto:jaulbach at nexant.com]
Sent: Friday, March 14, 2008 12:56 PM
To: Doebber, Ian; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Equest - Space Cooling Provided by Natural Gas!?
Somehow, you seem to have a chiller/heater specified. Are you SURE you
specified an electric chiller (you said CENTRAL chiller)?
John R. Aulbach, PE, CEM
Project Manager
Nexant, Inc.
701 West Kimberly Ave., Suite 245
Placentia, CA 92870-6342 USA
Phone: 714-524-4402
Fax: 714-524-4407
email: jaulbach at nexant.com
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Doebber,
Ian
Sent: Friday, March 14, 2008 11:40 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Equest - Space Cooling Provided by Natural Gas!?
I am modeling a New Orleans High School with a VAV system with Electric
Heat. The packaged rooftop units have Heating Hot Water Coils served by
a Center Boiler and Chilled Water Coils served by a Central Chiller.
For some strange reason, my summer and spring months have some space
cooling provided by Natural Gas Consumption. Since the boiler is the
only equipment consuming Natural Gas, how is the boiler providing
cooling? Very odd.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080314/ae4f27ff/attachment-0002.htm>
More information about the Bldg-sim
mailing list