[Bldg-sim] equest chilled water loop question-detailed edit mode
Aulbach, John
jaulbach at nexant.com
Tue Mar 25 13:07:58 PDT 2008
Christopher:
You need to be in the Detailed Edit mode to add individual loops and
cooling towers to individual chillers. In Detailed Edit Mode, go to the
Component Tree on the LH side, go to Water Side Tab on the top of the
screen. Then go to the Component Tree again on the "project"line above
the "Global Parameters" line, right click, and, behold, you can create
additional components (circulation loops, chillers, cooling towers, etc.
THIS is where you can create separate towers for separate chillers.
John
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Christopher
Sturdivant
Sent: Tuesday, March 25, 2008 11:37 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] equest chilled water loop question-detailed edit
mode
Greetings,
I was wondering if anyone knows the answer to this question. I
specified for three chillers and three cooling towers on my energy model
and when I go into the detailed edit mode it shows the three chillers
but it only shows one cooling tower. I was wondering why this was the
case and if it only shows one cooling tower then will it only take one
cooling tower in consideration during the simulation? Thank you very
much!
Christopher Sturdivant
Design Engineer-Mechanical
RMF Engineering, Inc.
Ph: 843-971-9639 ext. 110
Fax: 843-971-9641
csturdiv at rmf.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080325/e354bcf4/attachment-0005.htm>
More information about the Bldg-sim
mailing list