[Bldg-sim] Appendix G Baseline System for un-air conditioned zoo building
David S Eldridge
DSE at grummanbutkus.com
Thu May 15 13:01:52 PDT 2008
Is the room's ventilation controlled to maintain a maximum temperature for the animals, or only for ventilation rates?
However, I think there is a little bit of a disconnect in submitting the simulation as if it were cooled, and then having results with no cooling energy. Maybe this topic is suitable for a credit interpretation request?
David
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Allan Fox
Sent: Thursday, May 15, 2008 2:48 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Appendix G Baseline System for un-air conditioned zoo building
I am currently modeling a zoo building that is heated and ventilated only. According to ASHRAE 90.1 Appendix G, I have to model both heating and air conditioning even if no air conditioning exists. For this size building I have to model a System 3 - rooftop air conditioner with gas heat for both the base building and the proposed building. Is there anything in Appendix G that would prevent me from setting the cooling thermostat setpoint up to 90 degrees to prevent cooling energy from being included in the simulation as long as I use the same setting for both proposed and base models?
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080515/93c9cc1f/attachment-0002.htm>
More information about the Bldg-sim
mailing list