[Bldg-sim] Glass center-of-glass to assembly U-Value?

Josh Greenfield JGreenfield at primerachicago.com
Mon Sep 22 12:23:24 PDT 2008


ASHRAE 90.1-2004 Section 5.8.2.5 exception (b) allows the SHGC/SC
center-of-glass to be an acceptable alternative for determining
compliance with the SHGC/SC requirements for the overall fenestration
area.

 

 

 

Josh Greenfield, PE, LEED AP
Senior Associate
Primera Engineers, Ltd.
100 S. Wacker Drive, Suite 700
Chicago, IL 60606
312.606.0910 Main
312.242.6392 Direct
312.606.0415 Fax
jgreenfield at primerachicago.com
<blocked::mailto:jgreenfield at primerachicago.com> 
http://www.primerachicago.com <http://www.primerachicago.com> 

Be Green...please consider the environment before printing this email.

From: Zeng, Ming [mailto:mzeng at leoadaly.com] 
Sent: Monday, September 22, 2008 1:09 PM
To: Andrew Craig; Josh Greenfield; bldg-sim at lists.onebuilding.org;
equest-users at lists.onebuilding.org
Subject: RE: [Bldg-sim] Glass center-of-glass to assembly U-Value?

 

Can we use glass center of glass shading coefficient for the assembly ?
If not, is there any similar table for assembly shading coefficient
calculation? 

Thanks. 

 

Ming Zeng, PE, LEED(r) Accredited Professional
Mechanical Engineer

 
730 Second Avenue South, Suite 1100, Minneapolis, MN 55402-2455
T 612.338.8741    F 612.338.4840    D 612.341.9539    
www.leoadaly.com <http://www.leoadaly.com>     MZeng at leoadaly.com
<mailto:MZeng at leoadaly.com> 

 Please consider the environment before printing.

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Andrew
Craig
Sent: Monday, September 22, 2008 11:41 AM
To: Josh Greenfield; bldg-sim at lists.onebuilding.org;
equest-users at lists.onebuilding.org
Subject: Re: [Bldg-sim] Glass center-of-glass to assembly U-Value?

 

Attached is a handy spreadsheet from the Oregon Energy Code User's
Manual.  Hopefully this is what you are looking for.

 

Regards,

 

Please note my new e-mail address: andrewc at interfaceeng.com

Andrew Craig, EIT,LEED AP/ Mechanical Designer/ Energy Analyst
INTERFACE ENGINEERING 
direct 503.382.2696 

________________________________

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Josh
Greenfield
Sent: Monday, September 22, 2008 9:07 AM
To: bldg-sim at lists.onebuilding.org; equest-users at lists.onebuilding.org
Subject: [Bldg-sim] Glass center-of-glass to assembly U-Value?

 

Does anyone have any rules of thumb on a quick/easy approximation for
taking a Center-of-Glass U-value and converting it to an Assembly
U-value based on industry standard assembly constructions?  I know this
depends on a lot of variables, like frame material and conductance, and
the size of the overall glass assembly, etc., but I'm just looking for a
quick estimate on performance reduction for comparisons to other window
types for a particular building.

 

Also, is there an ASHRAE 90.1-2004 Baseline glass Visible Light
Transmittance (VLT)?

 

Josh Greenfield, PE, LEED AP
Senior Associate
Primera Engineers, Ltd.
100 S. Wacker Drive, Suite 700
Chicago, IL 60606
312.606.0910 Main
312.242.6392 Direct
312.606.0415 Fax
jgreenfield at primerachicago.com
<blocked::mailto:jgreenfield at primerachicago.com> 
http://www.primerachicago.com <http://www.primerachicago.com> 

Be Green...please consider the environment before printing this email.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080922/39de722e/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 476 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080922/39de722e/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 338 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080922/39de722e/attachment-0003.jpeg>


More information about the Bldg-sim mailing list