[Bldg-sim] Variable Speed Screw Chiller Curves
David S Eldridge
DSE at grummanbutkus.com
Wed Dec 2 08:39:44 PST 2009
You may want to run an eQuest report on the chiller to see how the efficiency is varying throughout the year. Output the load and the power at each hour and you should get a better idea of whether the curves are working or not, or if the default curves are reasonable for your specific equipment.
David
http://www.grummanbutkus.com
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Dan Russell
Sent: Wednesday, December 02, 2009 10:35 AM
To: Dan Nall; Kingsley,Michael L.; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Variable Speed Screw Chiller Curves
Well, I’m going over a year back into the archives, but hopefully someone can help. I’m modeling a project with 500 Ton Carrier Evergreen Water-Cooled Screw Chillers and would like to take advantage of the part-load efficiency benefits. It appears that Dan Nall posted custom efficiency curves for this specific equipment a while back, but when I use them in eQUEST my cooling energy gets tripled (from 800 MWh to 2450 MWh) as compared to the default eQUEST curves for Water-cooled Screw chillers. Does anyone have experience using these curves effectively? Am I misinterpreting the curve data? Are they intended for something other than eQUEST inputs? Or are the default eQUEST curves unrealistically efficient?
Thanks for any input,
Dan Russell
Engineering Incorporated
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Dan Nall
Sent: Tuesday, August 26, 2008 1:17 PM
To: Kingsley,Michael L.; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Variable Speed Screw Chiller Curves
Try these on for size;
"VFDSCrew EIR fPLR" = CURVE-FIT
TYPE = CUBIC
INPUT-TYPE = DATA
INDEPENDENT = ( 1, 0.75, 0.5, 0.25 )
DEPENDENT = ( 1, 0.97307, 1.01436, 1.3616 )
..
"Carrier-EIR-fCHWT&CWT" = CURVE-FIT
TYPE = BI-QUADRATIC-T
INPUT-TYPE = COEFFICIENTS
COEFFICIENTS = ( 0.767051, -0.0236208, 0.0004375, 0.0024939, 0.0002337,
-0.000418 )
..
"Carrier-EIR-fPLR&dT" = CURVE-FIT
TYPE = BI-QUADRATIC-RATIO&DT
INPUT-TYPE = COEFFICIENTS
COEFFICIENTS = ( -0.0230025, 0.902964, 0.0935993, 0.00347819,
-2.45759e-005, -0.00196462 )
..
"Carrier-CAP-fCHWT&CWT" = CURVE-FIT
TYPE = BI-QUADRATIC-T
INPUT-TYPE = COEFFICIENTS
COEFFICIENTS = ( 0.448509, 0.0185587, -0.00028125, 0.00306901,
-5.0201e-005, 0.000108475 )
-----Original Message-----
From: "Kingsley, Michael L."
Sent: Aug 26, 2008 2:15 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Variable Speed Screw Chiller Curves
Does anyone have DOE-2 performance curves for a variable speed screw chiller (I believe the Carrier Evergreen 23XRV is the only one now) that they would be willing to share?
Thanks in advance.
Michael Kingsley
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091202/a5a42aab/attachment-0001.htm>
More information about the Bldg-sim
mailing list