[Bldg-sim] IES-VE Energy
Benjamin Jordan
benmichaeljordan at gmail.com
Mon Feb 23 12:30:33 PST 2009
Varkie,
IES-VE is a great program to use for energy simulations and
qualifies for LEED simulations (EA Credit 1). Why use IES-VE? IES-VE
is very good for in-depth analysis of HVAC systems and their controls
(not strong on the water side, but very good on the air side). Also,
IES-VE creates great outputs (large selection, nice graphs, charts,
and more). Also, IES-VE creates an actual 3-D model that is nice to
have to visualize the actual building.
As far as Revit to IES plug-in, this is a different story. I have
found it easier to take 2D Cad files and extrude the DXF files. This
creates a much cleaner model that is much easier to change later. The
Revit Plug-in will work, but the Revit model must be drawn perfectly
with no errors. Also, the Revit model might need some tweaking before
converting to IES (I.E. if the Revit model has a columns in the middle
of a room that are surrounded by walls (common), then IES-VE will
recognize this as a hole in the model).
Next, IES also has a great support staff. If you run into any
problems, they are easy to contact and respond pretty quickly with the
solution.
Finally, IES-VE can be used for more than just energy simulations.
Detailed daylighting analysis, CFD analysis, regular lighting/glare
analysis, and more can all be done within IES.
Hope this helps.
Ben Jordan, E.I.T
Burt, Hill
On Mon, Feb 23, 2009 at 3:01 PM,
<bldg-sim-request at lists.onebuilding.org> wrote:
> Send Bldg-sim mailing list submissions to
> bldg-sim at lists.onebuilding.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> or, via email, send a message with subject or body 'help' to
> bldg-sim-request at lists.onebuilding.org
>
> You can reach the person managing the list at
> bldg-sim-owner at lists.onebuilding.org
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of Bldg-sim digest..."
>
>
> Today's Topics:
>
> 1. New IES-VE Mailing List on onebuilding.org called Virtual-sim
> (Jason Glazer)
> 2. Re: IES-VE Energy (CARNEY Ronan)
> 3. Re: IES-VE Energy (Stirling Walkes)
> 4. Re: IES-VE Energy (Varkie C Thomas)
>
>
> ----------------------------------------------------------------------
>
> Message: 1
> Date: Sun, 22 Feb 2009 14:52:16 -0600
> From: Jason Glazer <jglazer at gard.com>
> Subject: [Bldg-sim] New IES-VE Mailing List on onebuilding.org called
> Virtual-sim
> To: bldg-sim at onebuilding.org
> Message-ID: <49A1BB00.70406 at gard.com>
> Content-Type: text/plain; charset=ISO-8859-1; format=flowed
>
> Virtual-sim is a new mailing list is for everyone that uses
> the IES<VE> Virtual-Environment programs. Virtual-sim is a
> new mailing list on onebuilding.org joining program specific
> mailing lists for eQUEST, HAP, and TRACE. Users at every
> experience level are encouraged to join this mailing list
> and share their questions and knowledge. The mailing list
> will be a user-to-user support forum for IES<VE>, VE-ware
> and ApacheSim and other software by Integrated Environmental
> Solutions Ltd.
>
> To subscribe please send a blank email to:
>
> Virtual-sim-subscribe at onebuilding.org
>
> More information about IES<VE> is available at:
>
> http://www.iesve.com
>
> Please let me know if you have any questions.
>
> Jason
>
> --
> Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair
> Admin for onebuilding.org building performance mailing lists
>
>
> ------------------------------
>
> Message: 2
> Date: Mon, 23 Feb 2009 09:13:19 +1000
> From: "CARNEY Ronan" <Ronan.CARNEY at projectservices.qld.gov.au>
> Subject: Re: [Bldg-sim] IES-VE Energy
> To: "Stirling Walkes" <Swalkes at smseng.com>, "Varkie C Thomas"
> <thomasv at iit.edu>, "Bldg-Sim" <bldg-sim at lists.onebuilding.org>
> Message-ID:
> <29A586CC937CB64F8FE7AD0370913D23059CC6 at VBNEEXS01.dpwservices.dpw.qld.gov.au>
>
> Content-Type: text/plain; charset="iso-8859-1"
>
> I strongly advise you not to use this option. If Revit, looses a room, it's likely that you'll not even notice it. I created a full model of a 50million project within Revit from the Architectural model. Loaded it into IES and lost 75% of all rooms, that's over 200 rooms, all lost.
> My solution is, purchase the software, draw all model from sratch within IES of Sketchup, Stay away from IES with Revit, it always falls over or is incorrect or requires 3 or 4 times of repetitive data entry e.g. construction properties.
>
> Kind Regards
> Ronan Carney
>
> ________________________________
>
> From: bldg-sim-bounces at lists.onebuilding.org on behalf of Stirling Walkes
> Sent: Mon 23/02/2009 12:56 AM
> To: Varkie C Thomas; Bldg-Sim
> Subject: Re: [Bldg-sim] IES-VE Energy
>
>
> REVIT MEP comes with the IES VE load analysis built in. But I think you need to have the full version to analyze the energy consumption based on systems and lighting etc.
>
> I have found that as long as the spaces have been set up correctly by the architect in Revit generating the geometry for the energy model is done by Revit and takes a couple of minutes to determine interior vs exterior walls/windows etc. (depending on the size of the building and the capacity of the computer doing the calculations). The calculations will generate a room by room load calculation which can be imported back to the model and allocated to the individual spaces.
>
> Vs doing an import of the Autocad drawing and tracing the shape, locating windows etc. Time savings can be significant.
>
> However, I have only yet used it for loads for equipment sizing and not for an energy simulation.
>
> Regards,
>
>
>
> V. Stirling Walkes, P.Eng., LEED AP
> Partner
> SMS Engineering Ltd.
> 770 Bradford Street
> Winnipeg MB R3H 0N3 Canada
> phone: 204.775.0291
> fax: 204.772.2153
> Swalkes at smseng.com
>
>
>>>> Varkie C Thomas <thomasv at iit.edu> 2/21/2009 4:22 PM >>>
>
>
> I have been asked by an ME/AE firm to check out IES-VE Energy. This firm makes extensive use of the Revit programs for design.
>
> I downloaded the trial version of 'IES-VE-Ware/Toolkits 5.9 Setup' and tried to run/install it and I got the following message: "You require an installation of Google Stetchup 6, etc., to install VE-Ware"
>
> I downloaded 'IES<VE>5.9 SketchUp Plug-in Setup' and tried to install this and got the following message: "You must have a copy of IES<Virtual Environment>5.9 installed before attempting to install this plug-in"
>
> I am interested in trying out IES-VE Energy component only. Is there a trial version for this? Is there a tutorial that I can refer to when trying to learn how to use this program?
>
> The IES-VE website shows 2 engineering clients - Syska Hennessy and Vanderweil Engineering. How many building projects have been analyzed with IES-VE for energy performance by US AE firms?
>
> Why use IES-VE-Energy when DOE2.1E and eQUEST are free and TRACE and HAP are inexpensive with excellent customer support?
>
> Is there statistical data by type & size of project, on the energy programs used in the US for code compliance and LEED certification?
>
> Varkie Thomas
>
> ***************************** Disclaimer *****************************
>
> The contents of this electronic message and any attachments are intended only for the addressee and may contain privileged or confidential information. They may only be used for the purposes for which they were supplied. If you are not the addressee, you are notified that any transmission, distribution, downloading, printing or photocopying of the contents of this message or attachments is strictly prohibited. The privilege of confidentiality attached to this message and attachments is not waived, lost or destroyed by reason of mistaken delivery to you. If you receive this message in error please notify the sender by return e-mail or telephone.
>
> Please note: the Department of Public Works carries out automatic
> software scanning, filtering and blocking of E-mails and attachments (including emails of a
> personal nature) for detection of viruses, malicious code, SPAM, executable programs or content it deems
> unacceptable. All reasonable precautions will be taken to respect the privacy of
> individuals as outlined in the DPW Privacy Plan. Personal information will only be used for official
> purposes, e.g. monitoring Departmental Personnel's compliance with Departmental Policies.
> Personal information will not be divulged or disclosed to others, unless as required by Departmental
> Policy and/or State or Commonwealth Law.
>
> Thank you.
>
>
> ------------------------------
>
> Message: 3
> Date: Mon, 23 Feb 2009 11:09:55 -0600
> From: "Stirling Walkes" <Swalkes at smseng.com>
> Subject: Re: [Bldg-sim] IES-VE Energy
> To: "Varkie C Thomas" <thomasv at iit.edu>, "Bldg-Sim"
> <bldg-sim at lists.onebuilding.org>, "CARNEY Ronan"
> <Ronan.CARNEY at projectservices.qld.gov.au>
> Message-ID: <49A28403.C152.004B.0 at smseng.com>
> Content-Type: text/plain; charset="us-ascii"
>
> Thanks for the tip Ronan. Did you create a room schedule within Revit to monitor rooms and loads within rooms to ensure that they have been carried over properly? Or have you found that it isn't worth the time?
>
> Regards,
>
> Stirling
>
>
>>>> "CARNEY Ronan" <Ronan.CARNEY at projectservices.qld.gov.au> 2/22/2009 5:13 PM >>>
> I strongly advise you not to use this option. If Revit, looses a room, it's likely that you'll not even notice it. I created a full model of a 50million project within Revit from the Architectural model. Loaded it into IES and lost 75% of all rooms, that's over 200 rooms, all lost.
> My solution is, purchase the software, draw all model from sratch within IES of Sketchup, Stay away from IES with Revit, it always falls over or is incorrect or requires 3 or 4 times of repetitive data entry e.g. construction properties.
>
> Kind Regards
> Ronan Carney
>
> ________________________________
>
> From: bldg-sim-bounces at lists.onebuilding.org on behalf of Stirling Walkes
> Sent: Mon 23/02/2009 12:56 AM
> To: Varkie C Thomas; Bldg-Sim
> Subject: Re: [Bldg-sim] IES-VE Energy
>
>
> REVIT MEP comes with the IES VE load analysis built in. But I think you need to have the full version to analyze the energy consumption based on systems and lighting etc.
>
> I have found that as long as the spaces have been set up correctly by the architect in Revit generating the geometry for the energy model is done by Revit and takes a couple of minutes to determine interior vs exterior walls/windows etc. (depending on the size of the building and the capacity of the computer doing the calculations). The calculations will generate a room by room load calculation which can be imported back to the model and allocated to the individual spaces.
>
> Vs doing an import of the Autocad drawing and tracing the shape, locating windows etc. Time savings can be significant.
>
> However, I have only yet used it for loads for equipment sizing and not for an energy simulation.
>
> Regards,
>
>
>
> V. Stirling Walkes, P.Eng., LEED AP
> Partner
> SMS Engineering Ltd.
> 770 Bradford Street
> Winnipeg MB R3H 0N3 Canada
> phone: 204.775.0291
> fax: 204.772.2153
> Swalkes at smseng.com
>
>
>>>> Varkie C Thomas <thomasv at iit.edu> 2/21/2009 4:22 PM >>>
>
>
> I have been asked by an ME/AE firm to check out IES-VE Energy. This firm makes extensive use of the Revit programs for design.
>
> I downloaded the trial version of 'IES-VE-Ware/Toolkits 5.9 Setup' and tried to run/install it and I got the following message: "You require an installation of Google Stetchup 6, etc., to install VE-Ware"
>
> I downloaded 'IES<VE>5.9 SketchUp Plug-in Setup' and tried to install this and got the following message: "You must have a copy of IES<Virtual Environment>5.9 installed before attempting to install this plug-in"
>
> I am interested in trying out IES-VE Energy component only. Is there a trial version for this? Is there a tutorial that I can refer to when trying to learn how to use this program?
>
> The IES-VE website shows 2 engineering clients - Syska Hennessy and Vanderweil Engineering. How many building projects have been analyzed with IES-VE for energy performance by US AE firms?
>
> Why use IES-VE-Energy when DOE2.1E and eQUEST are free and TRACE and HAP are inexpensive with excellent customer support?
>
> Is there statistical data by type & size of project, on the energy programs used in the US for code compliance and LEED certification?
>
> Varkie Thomas
>
> ***************************** Disclaimer *****************************
>
> The contents of this electronic message and any attachments are intended only for the addressee and may contain privileged or confidential information. They may only be used for the purposes for which they were supplied. If you are not the addressee, you are notified that any transmission, distribution, downloading, printing or photocopying of the contents of this message or attachments is strictly prohibited. The privilege of confidentiality attached to this message and attachments is not waived, lost or destroyed by reason of mistaken delivery to you. If you receive this message in error please notify the sender by return e-mail or telephone.
>
> Please note: the Department of Public Works carries out automatic
> software scanning, filtering and blocking of E-mails and attachments (including emails of a
> personal nature) for detection of viruses, malicious code, SPAM, executable programs or content it deems
> unacceptable. All reasonable precautions will be taken to respect the privacy of
> individuals as outlined in the DPW Privacy Plan. Personal information will only be used for official
> purposes, e.g. monitoring Departmental Personnel's compliance with Departmental Policies.
> Personal information will not be divulged or disclosed to others, unless as required by Departmental
> Policy and/or State or Commonwealth Law.
>
> Thank you.
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090223/79f3b0d1/attachment.html>
>
> ------------------------------
>
> Message: 4
> Date: Mon, 23 Feb 2009 13:23:19 -0600
> From: Varkie C Thomas <thomasv at iit.edu>
> Subject: Re: [Bldg-sim] IES-VE Energy
> To: Stirling Walkes <Swalkes at smseng.com>
> Cc: Bldg-Sim <bldg-sim at lists.onebuilding.org>
> Message-ID: <e078ecc2e77c.e77ce078ecc2 at iit.edu>
> Content-Type: text/plain; charset="us-ascii"
>
> Thanks for the responses and telephone calls. Most of them were sent to me directly. The general picture I got was that TRACE700 does a better job of importing Revit data than IESVE. Importing and other problems can be fixed. Is the IESVE program in metric only?.
> Varkie
>
> ----- Original Message -----
> From: Stirling Walkes <Swalkes at smseng.com>
> Date: Monday, February 23, 2009 11:11 am
> Subject: RE: [Bldg-sim] IES-VE Energy
> To: Varkie C Thomas <thomasv at iit.edu>, Bldg-Sim <bldg-sim at lists.onebuilding.org>, CARNEY Ronan <Ronan.CARNEY at projectservices.qld.gov.au>
>
>> Thanks for the tip Ronan. Did you create a room schedule within
>> Revit to monitor rooms and loads within rooms to ensure that they
>> have been carried over properly? Or have you found that it isn't
>> worth the time?
>>
>> Regards,
>>
>> Stirling
>>
>>
>> >>> "CARNEY Ronan" <Ronan.CARNEY at projectservices.qld.gov.au>
>> 2/22/2009 5:13 PM >>>
>> I strongly advise you not to use this option. If Revit, looses a
>> room, it's likely that you'll not even notice it. I created a full
>> model of a 50million project within Revit from the Architectural
>> model. Loaded it into IES and lost 75% of all rooms, that's over
>> 200 rooms, all lost.
>> My solution is, purchase the software, draw all model from sratch
>> within IES of Sketchup, Stay away from IES with Revit, it always
>> falls over or is incorrect or requires 3 or 4 times of repetitive
>> data entry e.g. construction properties.
>>
>> Kind Regards
>> Ronan Carney
>>
>> ________________________________
>>
>> From: bldg-sim-bounces at lists.onebuilding.org on behalf of Stirling
>> WalkesSent: Mon 23/02/2009 12:56 AM
>> To: Varkie C Thomas; Bldg-Sim
>> Subject: Re: [Bldg-sim] IES-VE Energy
>>
>>
>> REVIT MEP comes with the IES VE load analysis built in. But I
>> think you need to have the full version to analyze the energy
>> consumption based on systems and lighting etc.
>>
>> I have found that as long as the spaces have been set up correctly
>> by the architect in Revit generating the geometry for the energy
>> model is done by Revit and takes a couple of minutes to determine
>> interior vs exterior walls/windows etc. (depending on the size of
>> the building and the capacity of the computer doing the
>> calculations). The calculations will generate a room by room load
>> calculation which can be imported back to the model and allocated
>> to the individual spaces.
>>
>> Vs doing an import of the Autocad drawing and tracing the shape,
>> locating windows etc. Time savings can be significant.
>>
>> However, I have only yet used it for loads for equipment sizing
>> and not for an energy simulation.
>>
>> Regards,
>>
>>
>>
>> V. Stirling Walkes, P.Eng., LEED AP
>> Partner
>> SMS Engineering Ltd.
>> 770 Bradford Street
>> Winnipeg MB R3H 0N3 Canada
>> phone: 204.775.0291
>> fax: 204.772.2153
>> Swalkes at smseng.com
>>
>>
>> >>> Varkie C Thomas <thomasv at iit.edu> 2/21/2009 4:22 PM >>>
>>
>>
>> I have been asked by an ME/AE firm to check out IES-VE Energy.
>> This firm makes extensive use of the Revit programs for design.
>>
>> I downloaded the trial version of 'IES-VE-Ware/Toolkits 5.9
>> Setup' and tried to run/install it and I got the following
>> message: "You require an installation of Google Stetchup 6, etc.,
>> to install VE-Ware"
>>
>> I downloaded 'IES<VE>5.9 SketchUp Plug-in Setup' and tried to
>> install this and got the following message: "You must have a copy
>> of IES<Virtual Environment>5.9 installed before attempting to
>> install this plug-in"
>>
>> I am interested in trying out IES-VE Energy component only. Is
>> there a trial version for this? Is there a tutorial that I can
>> refer to when trying to learn how to use this program?
>>
>> The IES-VE website shows 2 engineering clients - Syska Hennessy
>> and Vanderweil Engineering. How many building projects have been
>> analyzed with IES-VE for energy performance by US AE firms?
>>
>> Why use IES-VE-Energy when DOE2.1E and eQUEST are free and TRACE
>> and HAP are inexpensive with excellent customer support?
>>
>> Is there statistical data by type & size of project, on the energy
>> programs used in the US for code compliance and LEED certification?
>>
>> Varkie Thomas
>>
>> ***************************** Disclaimer *****************************
>>
>> The contents of this electronic message and any attachments are
>> intended only for the addressee and may contain privileged or
>> confidential information. They may only be used for the purposes
>> for which they were supplied. If you are not the addressee, you
>> are notified that any transmission, distribution, downloading,
>> printing or photocopying of the contents of this message or
>> attachments is strictly prohibited. The privilege of
>> confidentiality attached to this message and attachments is not
>> waived, lost or destroyed by reason of mistaken delivery to you.
>> If you receive this message in error please notify the sender by
>> return e-mail or telephone.
>>
>> Please note: the Department of Public Works carries out automatic
>> software scanning, filtering and blocking of E-mails and
>> attachments (including emails of a
>> personal nature) for detection of viruses, malicious code, SPAM,
>> executable programs or content it deems
>> unacceptable. All reasonable precautions will be taken to respect
>> the privacy of
>> individuals as outlined in the DPW Privacy Plan. Personal
>> information will only be used for official
>> purposes, e.g. monitoring Departmental Personnel's compliance with
>> Departmental Policies.
>> Personal information will not be divulged or disclosed to others,
>> unless as required by Departmental
>> Policy and/or State or Commonwealth Law.
>>
>> Thank you.
>>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090223/e934e42a/attachment-0001.htm>
>
> ------------------------------
>
> _______________________________________________
> Bldg-sim mailing list
> Bldg-sim at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>
>
> End of Bldg-sim Digest, Vol 15, Issue 21
> ****************************************
>
More information about the Bldg-sim
mailing list