[Bldg-sim] LEED Energy Modeling with eQUEST
Bishop, Bill
bbishop at PathfinderEngineers.com
Mon Jan 12 07:00:07 PST 2009
Hi Janne,
For figuring out the unmet load hours, the 300 hours per year is out of the 8,760 hours simulated. If every zone in the building simultaneously experiences an unmet load (such as when heating is first turned on after the building is allowed to get very cold), that only counts as one hour (or maybe two or three for a heat pump). The BEPS and BEPU DOE 2.2 reports show the percent of hours outside of throttling range. My understanding is that if this value is 3.4% or less (300/8760) than the condition is met.
Bill
William Bishop, EIT, LEED® AP | Pathfinder Engineers LLP
Mechanical Engineer
3300 Monroe Ave., Suite 306
Rochester, NY 14618
TEL (585) 218-0730 Ext. 114
FAX (585) 218-0737
bbishop at pathfinderengineers.com
www.pathfinderengineers.com
P Please consider the environment before printing this email
________________________________
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Kairento, Janne
Sent: Monday, January 12, 2009 9:36 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] LEED Energy Modeling with eQUEST
Hey All,
I am curious as to how to break up the thermal blocks in eQUEST. eQUEST allows each zone to be broken down into different space types by percentage. According to Appendix G, Table G3.1, Section 7, three conditions have to be met in order to clump thermal blocks together: the space use classification has to be the same, they have to have exposure to one façade (or a façade with a <45 deg bend), and they have to be served by the same type of HVAC equipment. When a large zone is created based on the area being conditioned by a HVAC system, breaking down the spaces by the percentage doesn't meet the three conditions required. If spaces are broken down according to the ASHRAE requirements, it often leads to a large amount of zones. If all zones have at least 1 hr. of unmet heating or cooling, and there are greater then 300 zones, the model will exceed the amount of hours allowed. Any suggestions on an approach on zoning to simplify the model that meets ASHRAE requirements?
Thanks,
Janne
Janne Kairento, E.I.T., LEED AP
Cosentini Associates
One Broadway
Cambridge, MA 02142
Phone: 617.494.9090
Fax: 617.494.9292
Please consider the environment before printing this e-mail
NOTICE OF CONFIDENTIALITY This E-mail message and its attachments (if any) are intended solely for the use of the addressees hereof. In addition, this message and the attachments (if any) may contain information that is confidential, privileged and exempt from disclosure under applicable law. If you are not the intended recipient of this message, you are prohibited from reading, disclosing, reproducing, distributing, disseminating or otherwise using this transmission. Delivery of this message to any person other than the intended recipient is not intended to waive any right or privilege. If you have received this message in error, please promptly notify the sender by reply E-mail and immediately delete this message from your system.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090112/d7fab790/attachment-0001.htm>
More information about the Bldg-sim
mailing list