[Bldg-sim] Appendix G Fan Power
James Hess
JHess at tmecorp.com
Thu Jul 2 08:43:10 PDT 2009
Gregg,
I appreciate the response.
I see what they are trying to do; I just don’t think it needs to be done. The total fan energy consumption (supply, return, exhaust) is the same for comparison purposes to the proposed design model.
On many projects, the baseline system is different than the proposed --> packaged single zone systems versus packaged VAV RTU, for example. Therefore, there would not be any return fans on the packaged single zone systems to allocate fan energy to. I don’t know if anyone is looking at this to that level of detail. Another separate issue is that the Appendix G fan energy equation way over estimates the fan energy associated with real packaged single zone systems, but I’ve posted previously on that issue and won’t bore anyone with those details.
I guess the bottom line is that if GBCI absolutely insists that the baseline fan energy be broken into components, we’ll come up with some kind of percentage allocation, similar to what you have done, as applied to the total baseline fan energy consumption for the sole purpose of filling out the template.
Thanks! ☺
Regards,
JAH
James A. Hess, PE, CEM
Energy Engineer
TME, Inc.
Little Rock, AR
ph 501-666-6776
cell 501-351-4667
jhess at tmecorp.com<mailto:email at tmecorp.com>
From: Gregg Liddick [mailto:gliddick at theepstengroup.com]
Sent: Thursday, July 02, 2009 9:35 AM
To: James Hess; Bldg-Sim
Subject: RE: [Bldg-sim] Appendix G Fan Power
Hi James,
As far as I’m concerned the main point of having project teams break the fan energy down into components is to ensure that the baseline fan power derived from the fan supply volume using Table G3.1.2.9 is not all attributed to supply fans if exhaust fans, return fans, etc. exist.
Regarding the breakdown, as far as I know you’re correct in that there is no guidance on that and what I do is take the percentages based on total fan power from the proposed case and apply it to the baseline case (e.g. 70% supply, 20% return, 10% exhaust).
Best Regards,
Gregg Liddick, EIT, LEED® AP
The Epsten Group, Inc.
429 Edgewood Avenue
Atlanta GA 30312
Phone: 404-577-0370 ext. 102
Fax: 404-577-1739
www.theepstengroup.com<http://www.theepstengroup.com>
Please consider the environment before printing this e-mail.
This transmission is intended exclusively for the individual or entity to which it is addressed. This communication may contain information that is confidential, proprietary, privileged or otherwise exempt from disclosure. If you are not the named addressee, you are NOT authorized to read, print, retain, copy or disseminate this communication, its attachments or any part of them. If you have received this communication in error, please notify the sender immediately and delete this communication from all computers. This communication does not form any contractual obligation on behalf of the sender, the sender's employer, or the employer's parent company, affiliates or subsidiaries.
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James Hess
Sent: Thursday, July 02, 2009 10:28 AM
To: Bldg-Sim
Subject: Re: [Bldg-sim] Appendix G Fan Power
We got a review comment on a recent LEED project asking us to break down the baseline HVAC power into components even though there is no direction, or requirement, from 90.1-2004 to do so.
Can someone please help me understand why this would be necessary?
LEED guidelines say we have to model per Appendix G, but Appendix G doesn't say we have to do this.
I do not think it is necessary to do this as the baseline total fan energy consumption numbers would still be the same.
The equation in Appendix G is meant to give a total allowance (for each system) for supply, return, and exhaust fans. It doesn't matter if we break the allowance down into components or not as the total fan energy consumption remains the same. Therefore, there is no value in doing this.
If we did break the fan energy numbers into components, how would we do that given that there is no direction from ASHRAE or LEED on how to do this?
Thoughts?
Regards,
James A. Hess, PE, CEM
Energy Engineer
TME, Inc.
On Jul 2, 2009, at 8:41 AM, "Jeremy Poling" <jpoling at epsteinglobal.com<mailto:jpoling at epsteinglobal.com>> wrote:
This issue will start to become a problem for anyone running energy models for LEED projects – reviewers on the new review teams are asking to see the total fan power for the baseline broken into individual components and reported as such in the template for Energy and Atmosphere Credit 1. The 90.1-2004 User’s Manual is also silent on the issue; however it raises another issue. In the example (Example G-J on page G-28) the calculations use total building supply CFM for an 80,000SF medical office building. Since the baseline is System 5 in that example and there would be multiple zones for the baseline, it appears that the equation should be used for the whole building only and not individual systems. Is this how you are applying the formulas? The user’s manual notes that fan powered VAV boxes are NOT included in the total fan power number as calculated from G3.1.2.9.
Jeremy R. Poling, LEED AP
Senior Sustainability Analyst
Strategic Services
Site Solutions | Operations | Sustainability
EPSTEIN
Architecture
Interiors
Engineering
Construction
Epstein is a firm believer in sustainability. We ask that you please consider the environment before printing this e-mail.
________________________________
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ellen Franconi
Sent: Thursday, July 02, 2009 7:37 AM
To: Vikram Sami; Bldg-Sim; Michael I Rosenberg
Subject: Re: [Bldg-sim] Appendix G Fan Power
At my firm, we proportion the baseline total fan power determined as an aggregated W/CFM based on the hp assigned to the fan motors (supply, return, exhaust) in the design documents. Of course this assumes that your baseline and your proposed design have a one-to-one fan correspondence.
Ellen
Ellen Franconi, Ph.D., LEED AP
Senior Energy Analyst
Architectural Energy Corporation
2540 Frontier Avenue
Boulder, CO 80301
tel. 303-444-4149
fax 303-444-4303
efranconi at archenergy.com<mailto:efranconi at archenergy.com>
http://www.archenergy.com/
>>> "Rosenberg, Michael I" <michael.rosenberg at pnl.gov<mailto:michael.rosenberg at pnl.gov>> 7/1/2009 4:48 PM >>>
You have calculated the kW/cfm correctly according to the 2004 version of Appendix G. The allowance actually goes up a little in 2007, for your case. As for the second part of your question, no you do not apply the same kW/cfm to the exhaust fan. The calculated allowed fan power the total allowed power for all fans that are part of the system, including the exhaust fan. The cfm component is based on the supply fan cfm only. Unfortunately, Appendix G gives no direction on how to divide the allowed fan power up among the various fans in the system.
Mike
__________________________
Michael Rosenberg
Senior Commercial Buildings Energy Analyst
ENERGY & ENVIRONMENT DIRECTORATE
Pacific Northwest National Laboratory
2032 Todd Street
Eugene, OR 97405
(541) 844-1960
michael.rosenberg at pnl.gov<mailto:michael.rosenberg at pnl.gov>
www.pnl.gov<http://www.pnl.gov>
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Vikram Sami
Sent: Wednesday, July 01, 2009 3:03 PM
To: Bldg-Sim
Subject: [Bldg-sim] Appendix G Fan Power
G3.1.2.9 Gives you a formula for calculating system fan electrical power for supply, return, exhaust and relief. Lets sat I have a zone with a PSZ-HP that has a supply volume of 1500 cfm. Using this formula along with table G3.1.2.9 I get a fan horse power of 1.29 and kW of 1.17. This equates to 0.00078 kW/cfm – which seems really high.
The second part to my question is assuming I have 500cfm of exhaust in this zone, do I apply the same kW/cfm to the exhaust fans as well as the return fans? It seems that the lower the fan volume the more inefficient the Appendix G values get from these tables.
Any guidance would be much appreciated.
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361
Responsive Design • Technological Expertise • Exceptional Service
Please visit our new website | www.lordaecksargent.com<file:///\\www.lordaecksargent.com\>
P Think GREEN before you print.
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090702/8d7d8677/attachment-0001.htm>
More information about the Bldg-sim
mailing list