[Bldg-sim] LEED / 90.1 Appendix G Base System Table
Robby Oylear
robbyo at rushingco.com
Tue Jun 23 08:11:20 PDT 2009
Appendix G seems to only specify that the cooling system (DX, CHW coils,
etc.) be modeled identical in the baseline and proposed buildings. If the
fan systems are different then I would assume the baseline building would
have a standard VAV fan that ramps up and down based on load, while your
proposed building will behave like a unit heater with cooling, cycling the
fans on and off to meet the load.
Does that answer your question?
Robby Oylear, LEED® AP
Mechanical Engineer
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Mike Kennedy
Sent: Monday, June 22, 2009 1:15 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] LEED / 90.1 Appendix G Base System Table
Hi All,
Washington State is thinking of using 90.1 Appendix G as the basis of
a performance path to it's commercial building energy
code. Looking at the base system table I was uncertain of how to
model the base system for a typical 100000sf warehouse with gas fired
unit heaters. Is there a common way to interpret the system
requirements for LEED modeling?
From building size the base system would be package VAV with
reheat. Since no cooling is installed in the proposed system the
fans on the faux cooling system must cycle. What was confusing is
that Appendix G requires I model the same cooling system in the
proposed. How does one model unit heaters with low fan power while
also modeling VAV cooling system?
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
More information about the Bldg-sim
mailing list