[Bldg-sim] Simulation of Central Plant for LEED 2.2 EA C1
Clark Denson
cdenson at ssr-inc.com
Fri Oct 2 14:02:51 PDT 2009
I've been interested in the topic of District Thermal Energy treatment,
as well.
My question concerns Step 1 (Building stand-alone scenario): In a
campus setting like a hospital, new buildings are typically served by an
existing CEP, and yet the new building is not charged a rate for CHW or
HW. The USGBC guidance indicates that in this case, "local market rates
as explained in the LEED v2.2 Reference Guide" should be used. However,
I have not found this data to be readily accessible, nor have I found
guidance in the LEED Reference Guide. In my most recent project in
Florida, I've been able to find District Chilled Water plants close to
the project site, but it is my understanding that there is not a single
District Hot Water or Steam Plant in the entire state!
What do I do in this case? And where in the LEED Reference Guide is the
"Treatment" referring to?
Thanks for your help,
Clark Denson
From: Seth P. Spangler [mailto:sspangle at rmf.com]
Sent: Friday, October 02, 2009 12:44 PM
To: Karen Walkerman; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Simulation of Central Plant for LEED 2.2 EA C1
Karen,
I gave a presentation on this subject with a member from USGBC and this
exact question was brought up. The answer was to use the local rate for
both systems. LEED/ASHRAE require that the energy rate be the same for
both the baseline and proposed designs. Fuel and electricity rates are
assigned using the local utility rate schedules as they would normally
apply to the building and using the normal ASHRAE and LEED modeling
rules. This line while a little ambiguous means that you should use the
rate that would be applied to the building if it was not connected to
the plant, not the discounted rate that the plant most likely receives.
Thanks
Seth Spangler, LEED(r) AP
Project Engineer
RMF Engineering, Inc
Ph: (843) 971-9639 ext:1497
Fax: (843) 971-9641
sspangle at rmf.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Karen
Walkerman
Sent: Tuesday, September 15, 2009 5:21 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Simulation of Central Plant for LEED 2.2 EA C1
Hi All,
I'm completing a model of a building that is heated by a central campus
steam plant for LEED NC 2.2 EA P1 and C1. I've followed the guidelines
in "Required Treatment of District Thermal Energy in LEED NC 2.2 and
LEED for Schools" dated May 28, 2008.
I'm doing pretty well, but I'm a bit confused by the following paragraph
(page 8 under the heading: Energy Model Implementation - Energy rates)
Step 2 (Aggregate Building / DES scenario) - in this modeling scenario
the DES-supplied energy is not
modeled as cost-neutral purchased energy, and thus purchased DES rates
(chilled water, steam, hot
water) are ignored. Fuel and electricity rates are assigned using the
local utility rate schedules as they
would normally apply to the building and using the normal ASHRAE and
LEED modeling rules. For
the Baseline Building the rates are applied to the code-compliant
heating or cooling plant as instructed
in Appendix G, and for the Proposed Building the rates are applied to
the virtual plant according to the
actual energy sources used in the upstream DES (electricity, gas, oil,
etc.).
They are a bit unclear...
If the central plant burns #6 oil, do you use the local rate for #6 oil
for the proposed system and the local rate for home heating oil for the
baseline?
OR
do you use the local rate for home heating oil for both?
Has anyone submitted one of these projects yet?
Thanks for your help.
--
Karen
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091002/5bdc8e36/attachment-0001.htm>
More information about the Bldg-sim
mailing list