[Bldg-sim] Easy Question
Wilson, Luke
LWilson at integral-group.net
Tue Apr 13 08:18:15 PDT 2010
John,
I'm assuming you are using ASHRAE 90.1-2007 Appendix G for your Baseline?
If so, the way I read it from Table G3.1 is that you should evenly distribute the WWR of the entire building, not for each floor. Therefore I would use 11.4% for each floor.
Luke
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Eurek, John S NWO
Sent: Tuesday, April 13, 2010 10:22 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Easy Question
I have a two story building. For the baseline I am evenly distributing the
fenestration.
The first floor window area is 462.2 ft^2
The second floor window area is 647.1 ft^2
The first floor wall area is 4858 ft^2
The second floor wall area is 4858 ft^2
In the base line model do I use:
First floor 9.5%
Second floor 13.3%
OR
First floor 11.4%
Second floor 11.4%