[Bldg-sim] HVAC system for semi-heated space under LEED
Jeremy Poling
jpoling at epsteinglobal.com
Tue Aug 31 15:13:38 PDT 2010
Just had this comment from a reviewer - the ASHRAE 90.1 handbook
explains this (it was page G-21 in the ASHRAE 90.1-2004 Handbook, but I
don't have the 2007 handbook to tell you that page number). For a
semi-heated space, the baseline building models only the heating portion
of the system. For an unconditioned space, the baseline has no system
modeled (any energy use is a penalty in the proposed model).
Conditioned spaces must be modeled based on the systems designed and the
baseline system per Table G3.1.1B; however, where a heating or cooling
system is not designed the proposed model must use the same system as
the baseline respectively (heating or cooling).
The semi-heated space heating system would need to comply with the
baseline system provisions for heating systems in Appendix G for the
baseline model and the proposed system would be modeled as it is
designed.
JEREMY R. POLING, PE, LEED AP
Associate Vice President,
Senior Sustainability Analyst
Strategic Services
Site Solutions | Operations | Sustainability
EPSTEIN
Epstein is a firm believer in sustainability. We ask that you please
consider the environment before printing this e-mail.
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Christian
Stalberg
Sent: Tuesday, August 31, 2010 4:45 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] HVAC system for semi-heated space under LEED
Assumption validation if you please ;^)
Under LEED, the HVAC system type for semiheated space
should be the same in both the baseline and the proposed
buildings, correct?
Thank you in advance!
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100831/4b98185d/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 252 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100831/4b98185d/attachment-0002.png>
More information about the Bldg-sim
mailing list