[Bldg-sim] Exhaust Fans in Baseline
Demba Ndiaye
Demba.Ndiaye at setty.com
Thu Jul 8 14:13:18 PDT 2010
Vinay,
It is required to also model the exhaust fans in the Baseline. Use same cfm and fan powers as in the Proposed.
______________
Demba NDIAYE
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Vinay Devanathan
Sent: Thursday, July 08, 2010 5:09 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Exhaust Fans in Baseline
Hello All,
Do we have to model the exhaust fans also according to Appendix G for a Baseline model?
If yes, how should we design the cfm?
Thank you very much.
Regards,
Vinay
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100708/85fd5128/attachment-0001.htm>
More information about the Bldg-sim
mailing list