[Bldg-sim] Exhaust Fans in Baseline
Vinay Devanathan
vinay.devanathan at gmail.com
Thu Jul 8 14:28:30 PDT 2010
Vikram,
Thanks for your reply.
So, does it mean I will have to model the exhaust fan in the baseline model
but in a fashion such that it consumes power proportionate to your proposed
design (supply, return and exhaust) but falls within the Allowable Fan
System bhp value of Appendix G. Am I right?
Thank you.
Regards,
Vinay
On Thu, Jul 8, 2010 at 5:23 PM, Sami, Vikram <Vikram.Sami at perkinswill.com>wrote:
> I'm pretty sure that your fan power allowance in 90.1 is for all fan
> energy (including exhaust). So for example if your baseline fan allowance is
> 20kW (hypothetical), you will need to apportion that allowance between
> supply and exhaust similar to your designed building.
>
>
>
> There was an extensive discussion about this around a year ago on this list
> (check the archives).
>
>
>
> *Vikram Sami*, LEED AP
>
> Sustainable Design Analyst
>
> 1382 Peachtree St. NE, Atlanta, GA 30309
>
> t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com
> www.perkinswill.com
>
> *Perkins+Will.* Ideas + buildings that honor the broader goals of society
>
>
>
>
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Vinay Devanathan
> *Sent:* Thursday, July 08, 2010 5:15 PM
> *To:* Demba Ndiaye
> *Cc:* bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Exhaust Fans in Baseline
>
>
>
> Demba,
>
> Thanks for your quick reply.
>
> Regards,
> Vinay
>
> On Thu, Jul 8, 2010 at 5:13 PM, Demba Ndiaye <Demba.Ndiaye at setty.com>
> wrote:
>
> Vinay,
>
>
>
> It is required to also model the exhaust fans in the Baseline. Use same cfm
> and fan powers as in the Proposed.
>
>
>
> ______________
>
> Demba NDIAYE
>
>
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Vinay Devanathan
> *Sent:* Thursday, July 08, 2010 5:09 PM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] Exhaust Fans in Baseline
>
>
>
> Hello All,
>
> Do we have to model the exhaust fans also according to Appendix G for a
> Baseline model?
> If yes, how should we design the cfm?
>
> Thank you very much.
>
> Regards,
> Vinay
>
>
>
> This email and any files transmitted with it are confidential and intended
> solely for the addressee. If you are not the named addressee you should not
> disseminate, distribute, copy, or alter this email.
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100708/3abaf289/attachment-0001.htm>
More information about the Bldg-sim
mailing list