[Bldg-sim] Infiltration
James V Dirkes II, PE
jvd2pe at tds.net
Fri Jul 2 09:41:36 PDT 2010
Dear Wookey,
A blower door test is probably the best way to get a good idea of
infiltration / leakage. It is, however, an extrapolation of a VERY limited
test. If you limit your test buildings to small and "airtight" (i.e.,
constructed purposefully by a knowledgeable contractor to be tight) and the
HVAC system does not affect the building pressure, the blower door probably
does a good job. I was thinking of a much broader type of building.
The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Wookey
Sent: Friday, July 02, 2010 11:28 AM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Infiltration
+++ James V Dirkes II, PE [2010-07-02 09:47 -0400]:
> Amen to that!
>
> Stated another way, almost anyone who thinks they know (with any
precision) the
> infiltration rate of any building is misinformed.
Do you not feel that door blower tests on small, airtight domestic
buildings, as required for passivhaus certification, are not
reasonably accurate?
I quite agree that for large or very leaky buildings there is a real
problem, but I don't agree that there is no such thing as
sufficiently-accurate testing, and the passivehaus people are nothing
if not careful and rigorous about the science.
Wookey
--
Principal hats: Linaro, Emdebian, Wookware, Balloonboard, ARM
http://wookware.org/
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
More information about the Bldg-sim
mailing list