[Bldg-sim] LEED & Natural Ventilation
Rimes, Christie
Christie.Rimes at wspfk.com
Thu Jul 29 11:40:54 PDT 2010
eQuest, TAS and IES, I know can model natural ventilation. In IES and
TAS you can actually model the operation of the windows by defining
limits on indoor temperature, wind speeds etc. eQuest is a little more
basic where you can use a S-G function for infiltration which calculates
higher infiltration rates based on outside wind conditions. eQuest then
calculates if indoor temperatures will be kept between the indoor
temperatures based on the outside conditions. If yes than it will shut
off the mechanical system and calculate 0 energy for that hour.
Therefore in programs like IES and TAS you may be able to keep
conditions below the set point even if the outdoor temperatures are
hotter due to air movement etc. You may also want to come to an
agreement with the client to allow a slightly higher set point, however
you will need to also apply this to the baseline model. Otherwise for
LEED, you can't take account for the hours were naturally ventilation
doesn't provide comfort. Also note that the unmet load hours can be a
maximum of 300 hours so potentially you could take credit for 300 hours
for natural ventilation even if it is above the set point.
From: Chris [mailto:floodyc at gmail.com]
Sent: Thursday, July 29, 2010 11:24 AM
To: Rimes, Christie
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] LEED & Natural Ventilation
And how did you model the natural ventilation?
In summer when external temperatures are above the room setpoint natural
ventilation during the day would not provide any cooling.
On Thu, Jul 29, 2010 at 11:19, Rimes, Christie <
Christie.Rimes at wspfk.com> wrote:
I am currently doing a naturally ventilated building for LEED and I
believe that if the space is achieving indoor temperatures between the
given set point using natural ventilation than the mechanical system
energy is 0 for the proposed design. Any hours where natural ventilation
can't achieve indoor temperatures within the set points, a mechanical
system needs to be modeled even if there isn't one in the proposed
building. This helps keep the unmet hours within the requirements for
LEED.
Cheers,
From: bldg-sim-bounces at lists.onebuilding.org [mailto:
bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Chris
Sent: Thursday, July 29, 2010 11:13 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] LEED & Natural Ventilation
All,
we regularly design and model buildings which rely in part on natural
ventilation as a source of free cooling. The issue we are often faced
with is how to capture this benefit when performing a LEED Appendix G
analysis. Appendix G states that all conditioned spaces must have BOTH
heating and cooling. We would like to remove mechanical coolig in the
proposed design building and thus gain benefit when comparing to the
mechanical cooling system in the reference baseline building.
Has anyone tackled this issue and come to a satisfactory resolution?
Thanks for your help.
--
Chris Flood BSc (Eng)
Senior Building Analyst & Energy Modeller
--
Chris Flood BSc (Eng)
Senior Building Analyst & Energy Modeller
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100729/63eb56c6/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 10665 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100729/63eb56c6/attachment-0002.png>
More information about the Bldg-sim
mailing list