[Bldg-sim] 90.1-2004/2007 Baseline Question
Zoeteman, Mark R.
mrzoeteman at FTCH.com
Wed Mar 10 06:03:36 PST 2010
Nick,
Appendix G indicates Baseline Building "Floors" are to be Steel-joist. Refer to Climate Building Envelope Requirement tables in Section 5 and use U-factor for Steel-joist Floor for your climate zone.
Mark Zoeteman, FTC&H
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Tuesday, March 09, 2010 8:19 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] 90.1-2004/2007 Baseline Question
I've stumped myself!
When building a baseline model using 90.1-2004 or 2007, what envelope construction properties should we use for floors exposed to the exterior?
I'm currently planning on the "if all else fails match the proposed" route, but does there exist any guidance from ASHRAE or other sources regarding what the baseline case would be for such envelope elements?
~Nick
[cid:image001.jpg at 01CAC030.91AB0D30]
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100310/f10952ef/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100310/f10952ef/attachment-0002.jpg>
More information about the Bldg-sim
mailing list