[Bldg-sim] EE4 - Packaged VAV with Fan Powered Boxes
Chris Jones
cj at enersave.ca
Fri Nov 19 04:18:01 PST 2010
You can't directly model this system in EE4. The only solution is to
create your project in EE4 then edit the proposed .DOE file to add in
the series fan powered box statements at each zone. You then have to
run the file from the command line.
At 05:04 PM 17/11/2010, Brian Tysoe wrote:
>Content-Language: en-US
>Content-Type: multipart/alternative;
>
>boundary="_000_89B4FB2D5DE7614EB31CD320ED5249581E6B1F08DATORSVREX5mcwc_"
>
>Hi,
>
>I am trying to model a packaged VAV rooftop unit with fan-powered
>boxes in the perimeter zones. After hours the RTU fans are off and
>the fan-powered boxes cycle to maintain the night setback temperature.
>
>How can I correctly model the fan energy for this system in EE4?
>
>When I select "Packaged VAV" as my system type there is no option to
>enter any fan energy at the zone level.
>
>What should I use for a fan schedule and what should I put under
>"Fan Operation" at the system level?
>
>Currently I do not have the terminal fans entered anywhere, just the
>RTU fans. I am not sure if I am over estimating the fan energy
>because the RTU fans are cycling to maintain night setback; or if I
>am under estimating the fan energy because there are no fans
>operating at night.
>
>Also, if I have an exhaust fan in my RTU in addition to the supply
>fan and return fan, should I include it with my supply fan or with
>my return fan?
>
>Thanks,
>
>
>Brian Tysoe M.A.Sc., P.Eng., LEED AP
>Mechanical Engineer
>
><http://www.mcw.com>MCW Consultants Ltd.
>600-156 Front Street West
>Toronto, ON M5J 2L6
>Phone 416-598-2920
>Fax 416-598-5394
>
>This e-mail may be privileged and confidential. Any unauthorized use
>is strictly prohibited. If you received this e-mail in error, please
>contact the sender directly.
>
>
>----------
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
Chris Jones
14 Oneida Avenue
Toronto, ON M5J 2E3.
Tel. 416-203-7465
Fax. 416-946-1005
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101119/236e13aa/attachment-0002.htm>
More information about the Bldg-sim
mailing list